I have a Cerbo GX connected to a MultiPlus-II 48/5000/70-50, ESS enabled.
I’m looking for a way to force solar power into my EV rather than using it to charge the house battery.
Right now, I can only get 2kw of power from the solar panel. If I increase the vehicule charging power, then the additional power is taken from the grid instead of the solar panels.
8A charging seems to be the limit :


If I increase the power of the charging vehicule (here to 12 A), it starts draining power from the grid instead of using solar :

Do you still have DESS turned on as well?

8 A × 230 V ≈ 1.85 kW, so your “2 kW limit” matches the 8 A almost exactly. It looks less like a PV limit and more like the system only covering part of the load. A few things to check:

  1. Where is the EV charger connected, AC-in or AC-out side? If it’s on the AC-in side and you have no grid meter (ESS “Grid metering” set to Inverter/charger), ESS can’t see that load at all, and the grid supplies it. Either move it to AC-out or add an energy meter.
  2. ESS → Limit inverter power: check that it isn’t set to around 2 kW.
  3. Are the panels on an MPPT (DC-coupled)? When the battery is full and nothing pulls the power, the MPPT throttles down. Check the MPPT power when you start charging at 12 A: does it ramp up or stay flat?
  4. As Peter asked: make sure DESS is off, otherwise it overrides ESS behaviour.

A screenshot of the overview while charging at 12 A (PV, battery, AC loads, grid) would show which one it is.

1. The EV charger is on the AC-in (right now there is no load on AC-out). I have an ET340 meter on the grid that is working fine, for any other scenario it is clear that the cerbo has the information and uses it to avoid any injection to the grid.
2. I have not set any limit on the inverter power (it’s off)
3. Panels are on MPPT, DC coupled. When I increase EV charging power, MPPT power stays flat (it’s already at max, in bulk mode, blue light), it’s just that it continues to charge the house battery instead of using this power for the house load.
4. DESS is ON, my understanding is that I need this to take into consideration the changes in grid prices (I have a “Tempo” contract) ?

The second screenshot is done with charging at 12A, you can see that the power generated by the panels is split in half between the house battery and the AC load. There is enough solar power to cover for all the load, but the algorithm chooses to charge the battery at the same time and drain this power from the grid.

I solved the issue just by increasing the Grid current limit from 10 to 32A