# Essential Loads reading shows wrong load

**URL:** <https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081>\
**Category:** DIY\
**Tags:** pv-inverter, pv\_inverter, multiplus-ii, diy\
**Created:** [14 November 2026 11:42 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081 "2026-11-14T11:42:26Z")\
**Posts on this page:** 15\
**Page:** 1

<div class="post-metadata">

**Author:** ![Marrcin](https://avatars.discourse-cdn.com/v4/letter/m/ecb155/32.png) [@Marrcin](https://community.victronenergy.com/u/Marrcin)\
**Post date:** [14 November 2026 11:42 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/1 "2026-11-14T11:42:27Z")

</div>

In my off-grid Victron system with a Fronius inverter on AC-out, the “Essential Loads” reading shows wild, unstable spikes despite a completely steady real household load. This issue just started happening recently even though the system has been running stable for months without any changes. Has anyone experienced this problem?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [14 November 2026 14:46 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/2 "2026-11-14T14:46:14Z")

</div>

Do you have the system set up with loads on the AC input and out put checked?

---

<div class="post-metadata">

**Author:** ![Marrcin](https://avatars.discourse-cdn.com/v4/letter/m/ecb155/32.png) [@Marrcin](https://community.victronenergy.com/u/Marrcin)\
**Post date:** [14 November 2026 16:48 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/3 "2026-11-14T16:48:02Z")

</div>

yes, fronius is at AC Out

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 November 2026 16:55 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/4 "2026-11-14T16:55:31Z")

</div>

The system has to calculate the values at AC Out somehow. But if your Fronius is constantly providing different yield values at the output, the calculations will jump around too. Are you still using MPPTs or only charging via the Multis? How is the Fronius connected?

---

<div class="post-metadata">

**Author:** ![Marrcin](https://avatars.discourse-cdn.com/v4/letter/m/ecb155/32.png) [@Marrcin](https://community.victronenergy.com/u/Marrcin)\
**Post date:** [14 November 2026 17:02 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/5 "2026-11-14T17:02:03Z")

</div>

Fornius at AC Out  
MPPT still in system

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 November 2026 17:04 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/6 "2026-11-14T17:04:31Z")

</div>

… I see 😋 … but is this measured separately using a counter? Or a script?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [14 November 2026 17:06 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/7 "2026-11-14T17:06:24Z")

</div>

No there is a setting to do with AC loads position. Check that

---

<div class="post-metadata">

**Author:** ![Marrcin](https://avatars.discourse-cdn.com/v4/letter/m/ecb155/32.png) [@Marrcin](https://community.victronenergy.com/u/Marrcin)\
**Post date:** [14 November 2026 17:09 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/8 "2026-11-14T17:09:00Z")

</div>

I dont use any energy meter, power calc by victron

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 November 2026 17:16 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/9 "2026-11-14T17:16:41Z")

</div>

… and the AC Out isn’t counted, it’s only calculated. But if power from the AC Out and the Fronius is flowing into the Multi to charge it, while you also have loads on the AC Out, things will fluctuate because the PV conditions at the AC Out are constantly changing.

---

<div class="post-metadata">

**Author:** ![Marrcin](https://avatars.discourse-cdn.com/v4/letter/m/ecb155/32.png) [@Marrcin](https://community.victronenergy.com/u/Marrcin)\
**Post date:** [14 November 2026 17:21 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/10 "2026-11-14T17:21:50Z")

</div>

do You mean that settings:?

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/9/d/9d5d65ea39d6922d210491324f848bacafd85145.png)

---

<div class="post-metadata">

**Author:** ![Netrange](https://avatars.discourse-cdn.com/v4/letter/n/7ab992/32.png) [@Netrange](https://community.victronenergy.com/u/Netrange)\
**Post date:** [14 November 2026 17:24 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/11 "2026-11-14T17:24:09Z")

</div>

Just set it to AC Out … but I think that’s now only for the display in VRM … then the loads window BEFORE the Multi disappeared … that was always a nuisance when operating without a real AC In …

---

<div class="post-metadata">

**Author:** ![dognose](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dognose/32/968_2.png) [@dognose](https://community.victronenergy.com/u/dognose)\
**Post date:** [14 November 2026 18:37 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/12 "2026-11-14T18:37:59Z")

</div>

Why is there a grid on ac input 1 in a off-grid system? If some meter is accidently configured as “Grid” that may cause all sort of strange calculations.

---

<div class="post-metadata">

**Author:** ![Marrcin](https://avatars.discourse-cdn.com/v4/letter/m/ecb155/32.png) [@Marrcin](https://community.victronenergy.com/u/Marrcin)\
**Post date:** [14 November 2026 18:49 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/13 "2026-11-14T18:49:04Z")

</div>

Because I have the grid as a backup (with a Victron energy meter configured as a grid meter), but the grid is not connected to the MultiPlus

---

<div class="post-metadata">

**Author:** ![dognose](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dognose/32/968_2.png) [@dognose](https://community.victronenergy.com/u/dognose)\
**Post date:** [14 November 2026 18:53 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/14 "2026-11-14T18:53:59Z")

</div>

That is a bad idea, you should only have the grid meter connected and visible to the system, while the system is grid connected. If it isn’t, drop the meters connection. Else, several things may use readings from the grid meter, which do not fit into the real systems layout.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [15 November 2026 05:25 UTC](https://community.victronenergy.com/t/essential-loads-reading-shows-wrong-load/65081/15 "2026-11-15T05:25:55Z")

</div>

This explains the essential loads. Usually that is not metered separately if everything is on the output of the inverter and the system is actually off-grid.

And you have only got loads on the AC out, but it is set the system differently.