I can’t get it to feed power into the grid. The MultiPlus regulates to 0. No matter what I set, whether “BatteryLife” or “No BatteryLife”, it supplies the load from the grid, including losses, and only uses the solar power generated to charge the batteries. The battery is currently full. The MPPT switches to minimum.
The system was checked by a professional. He can’t find anything wrong either.
What can I change to make this work, or does it generally not work with lead-acid batteries?
You need to set the physical switch at the bottom of the MP to “Inverter & Charger” (I). It looks like you have it set to “Charger only” (II). (Then nothing comes out of the Multi.)
Bear in mind that when changing the setting, you’ll pass through the “Off” position
Hello
I’ve now restarted VE-Configure 3 to save the configuration. It told me there was a new version available. It also required an update to the ESS Assistant. After that, I loaded everything again and now it works. It’s feeding power into the grid at full capacity. My setpoint of -200 W doesn’t seem to matter at the moment, though.
I didn’t have this update, 90.04.248, the day before yesterday.
Thanks anyway!
The switch was already in the correct position.