ESS schedule start during grid loss event shuts down all multiplus hard

Hi,

Today my system is in a grid loss event thus the victron system goes in emergency mode. All loads are properly serviced from the battery and pv is stored in the battery.

So far so good.

However, I also have a schedule at 22:02 to load the battery to 50% in 5:50 hours.

Still with a SOC of 69% and coming at around 22:00 the system hard shuts down without error or anything in the logs or VRM. All three multiplusses are off.

Since the SOC is way above the threshold of 50% no charging should take place. Assuming the schedule would not try to offload SOC above 50% to grid while the grid is not there, also makes no sense to me.

Surely the ESS schedule is not trying to trigger anything when is a grid loss situation and if so wouldn’t that be a bug?

Anyone has a idea why the combination grid loss and ESS schedule could hard shutdown the whole 3 phase victron system?

Thanks, F.

It would have nothing to do with scheduled charge. Features of ESS Fall away when grid goes out.

Sometimes the soc is wrong as well. Are they can connected batteries?

What was the battery voltage? Was the system at the configured shut down voltage?

And did the battery send a DCL of zero to the system?

Hi,

Batteries are bms can connected pylontechs. Having around 49.34 voltage. Lowest cell 3.289 and highest 3.291. 6 US5000 charged to 100% about 3 weeks ago, there is a slight soc drift between the batteries max 70 and lowest 64, at the moment it went out we used around 800W so nothing major.

Was the system at the configured shut down voltage?

Not sure, would that be directy in the multiplusses via VEConfigure (need to get those then).

DCL of zero

That I do not know.

I was only able to restart the system providing back the grid (grid lost was actually a phase loss) so when getting back power on two phases the multiplusses start again.

I have left the system as is and the loads are back on the phases from the grid rather than battery.

It would have nothing to do with scheduled charge. Features of ESS Fall away when grid goes out.

That would be as I expect it, but I have been running the whole day on emergency power with no problem. The timing, system goes out when schedule is triggered to start seems too much of a coincidence to be not connected. Could be a bug also.

grid should be fixed for me today if all is well, but any suggestions I should start looking at?

This morning, as test, I disconnected the grid from the inverters and they happily keeping up AC-out while AC-IN is not available..

If it would be shutoff voltage than it would have shut off already I assume…

Have you tried turning the grid off and adding a schedule charge to come on a minute later as a test?

I agree with @LX. I think it’s an unfortunate coincidence. The schedule charge shouldn’t bring the system down if it was already off grid.

If all your dynamic cut offs were set up as prescribed and the DC shut down, then it could not have been the system doing it.
There has to be a different factor.

Was this with or without load?

Then how does the bank voltage compare with the vehicle bus voltage-this being what the inverter works with in the physics reality.

Hi,

Thanks for the tips to look at or to do next.

Have you tried turning the grid off and adding a schedule charge to come on a minute later as a test?

Will do this over the weekend.

Was this with or without load.

That was with no load.

The numbers from the moment of the shutdown are:

  • max cell: 3.279
  • min cell: 3.277
  • bus voltage: 49.170

Over the summer the system discharged to 20% with no problems.

The only recent change (due to raising min soc to 50 for winter) is enabling the load schedule.

The cerbo logged following errors:

  • #1 Device switched of (this is the multiplus attached to the lost phase) - expected
  • #3 Excepted devices error

Home assistent did not show any other alarms than grid lost.

  1. VEConfigure Settings - Victron & Pylontech

The system was setup in 2023 and configured to the settings advised back then.

I will extract the configuration again and re-verify against the latest version.

Thanks, Tran