# ESS ignores grid setpoint, feed-in limit and Min SOC – 9x Quattro 3-phase system exporting battery t

**URL:** <https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535>\
**Category:** Q&A and troubleshooting\
**Tags:** pv-inverter, 3-phase, parallel, dess, cerbo\_gx, professional, cerbo-gx\
**Created:** [29 October 2026 17:26 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535 "2026-10-29T17:26:48Z")\
**Posts on this page:** 8\
**Page:** 1

<div class="post-metadata">

**Author:** ![cmarazzi](https://avatars.discourse-cdn.com/v4/letter/c/a6a055/32.png) [@cmarazzi](https://community.victronenergy.com/u/cmarazzi)\
**Post date:** [29 October 2026 17:26 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/1 "2026-10-29T17:26:48Z")

</div>

Hello,

We have an ESS system that is discharging the battery into the grid. It ignores the grid setpoint, the feed-in limit and the minimum SOC. I’d appreciate your help diagnosing it.

SYSTEM

- 9x Quattro 48/10000/140-2x100 120V, 3 per phase, 208/120V 3-phase
- Phase masters: L1 HQ2243RK9HV, L2 HQ2146XUMEZ, L3 HQ2133RUDYN
- Cerbo GX, firmware 3.85, image type Normal (no Node-RED)
- Grid on AC-in 2; generator on AC-in 1
- BSLBATT LFP bank (~8,000 Ah) with BMS on the Cerbo (CVL 56.0 V); DVCC forced on, max charge 310 A / 55.1 V
- 3x Fronius 15K AC-coupled on AC-out
- VRM site: Hipodromo

ESS SETTINGS

- Mode: Optimized (without BatteryLife)
- Grid metering: Inverter/Charger (no external meter)
- Multiphase regulation: Total of all phases
- Grid setpoint: 0 W; Minimum SOC: 55%
- Peak shaving: Always, no import/export limits
- Dynamic ESS: not configured
- VEConfigure: ESS is the only assistant; core settings identical on all 9 units

SYMPTOM  
In Optimized mode, the system discharges the battery and exports roughly 16–19 kW to the grid on all three phases. Example: Grid -18.9 kW, loads 40.5 kW, PV 9.7 kW, battery -47 kW at 94% SOC. We get no credit for export, so this is a pure loss.

TESTS PERFORMED (Oct 29, 2026)

1. Disabled Modbus TCP and MQTT on the Cerbo: no change.
2. Grid feed-in limit enabled at 0 W (“Feed-in limiting active: Yes”): still exporting about 16 kW.
3. Minimum SOC raised to 95% with SOC at 92% (ESS #1, discharge disabled): battery still discharging about 17 kW.
4. Mode “Keep batteries charged”: system responds correctly and charges from the grid.

The Quattros consistently deliver about 19 kW more battery power than ESS requests, regardless of the setpoint. The BMS current matches the Quattro AC power, so the discharge is real, not a reporting error.

HISTORY  
About a week ago we had VE.Bus Error 19 when the generator stopped. One Quattro on L2 showed abnormal LEDs and is a suspect unit. No breakers tripped.

ATTACHED

- Remote VEConfigure file (.rvms)
- Screenshots of the overview, ESS, DVCC, feed-in and BMS parameter pages

QUESTIONS

1. What could make the phase masters ignore the ESS setpoint, feed-in limit and discharge-disabled state while still obeying “Keep batteries charged”?
2. Is a VE.Bus system reset or firmware reflash recommended, and is there a way to do it without dropping critical loads?  
Thank you,

Carlo

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [29 October 2026 18:19 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/2 "2026-10-29T18:19:11Z")

</div>

> [@cmarazzi](#):
>
> that is discharging the battery into the grid. It ignores the grid setpoint, the feed-in limit and the minimum SOC.

> [@cmarazzi](#):
>
> 1. Grid feed-in limit enabled at 0 W (“Feed-in limiting active: Yes”): still exporting about 16 kW.

Do you or don’t you want to feed into grid?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [29 October 2026 18:20 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/3 "2026-10-29T18:20:27Z")

</div>

> [@cmarazzi](#):
>
> 1. Disabled Modbus TCP and MQTT on the Cerbo: no change.

> [@cmarazzi](#):
>
> - 3x Fronius 15K AC-coupled on AC-out

Modbus is needed or the fronius control.

Are they se up right? Do they feed in?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [29 October 2026 18:21 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/4 "2026-10-29T18:21:53Z")

</div>

> [@cmarazzi](#):
>
> ATTACHED
> 
> - Remote VEConfigure file (.rvms)
> - Screenshots of the overview, ESS, DVCC, feed-in and BMS parameter pages

They aren’t uploaded

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [29 October 2026 18:22 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/5 "2026-10-29T18:22:29Z")

</div>

> [@cmarazzi](#):
>
> QUESTIONS
> 
> 1. What could make the phase masters ignore the ESS setpoint, feed-in limit and discharge-disabled state while still obeying “Keep batteries charged”?
> 2. Is a VE.Bus system reset or firmware reflash recommended, and is there a way to do it without dropping critical loads?  
> Thank you,

1. Mostly programming and set up. Something (or a few something’s) was missed.
2. No. You cannot reprogram or update without power disruption

> [@cmarazzi](#):
>
> - Multiphase regulation: Total of all phases

Try this as individual phase regulation. With the set point at 0.  
It is very possible you have massively unbalanced phases

---

<div class="post-metadata">

**Author:** ![cmarazzi](https://avatars.discourse-cdn.com/v4/letter/c/a6a055/32.png) [@cmarazzi](https://community.victronenergy.com/u/cmarazzi)\
**Post date:** [29 October 2026 18:57 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/6 "2026-10-29T18:57:32Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/3/6/36635f07cf647bbd06a0698fae558248cf3a777d.png)

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [29 October 2026 18:59 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/7 "2026-10-29T18:59:29Z")

</div>

> [@cmarazzi](#):
>
> 1. state while still obeying “Keep batteries charged

If you have told it to keep the batteries charged that is what it will do- charge them.  
Expected behaviour.

Are you exceeding an input current limit- explain your complaint here. It seems like it is close to matching your load anyway. So it is barely above that base load.

> [@cmarazzi](#):
>
> - Grid setpoint: 0 W; Minimum SOC: 55%

And very different to this setting which prioritises self consumption

---

<div class="post-metadata">

**Author:** ![cmarazzi](https://avatars.discourse-cdn.com/v4/letter/c/a6a055/32.png) [@cmarazzi](https://community.victronenergy.com/u/cmarazzi)\
**Post date:** [29 October 2026 23:23 UTC](https://community.victronenergy.com/t/ess-ignores-grid-setpoint-feed-in-limit-and-min-soc-9x-quattro-3-phase-system-exporting-battery-t/64535/8 "2026-10-29T23:23:36Z")

</div>

[Hipodromo\_48e7da85a779\_inst\_ttyS4\_Interfaces\_Mk2\_Tunnel-3.rvms](https://community.victronenergy.com/uploads/short-url/md5zURGqTuL51tctKqbv7GfmtF1.rvms) (13.2 KB)

I do not what to sell to the grid, I only want to charge from PV.