Although an excellent question, the answer is unfortunately: “…it depends”.
Mostly because rules and regulations between countries differs and sometimes there’s room for interpretation, certain protections are “recommended” not required. That’s why it depends…
Not aware of the requirements in the UK, let’s approach your question from an Electronic Physics perspective or simply decent circuit design in general. First you need to protect devices and cables against overcurrent and shortcircuits, second, depending on how much you care about a human life, you should protect the system against ground faults. The former is done with a MCB, the latter with a RCD or combined with a RCBO. So in general, connecting a device to a grid should have a MCB and RCD, now the real fun starts…
With an inverter device, like a Victron MultiPlus, that delivers power on its own (from the battery) things are getting a bit more complicated. You have a grid that delivers power and now there’s another device, your Victron Inverter, that’s also delivering power to the same circuit, in parallel to the grid (AC-IN) or serial (AC-OUT). You need to take that “extra” power (things like Power Assist) into account choosing your MCB’s and RCD’s. It’s comparable with the last decade of PV installations, where 35A grid connections get extended with 16A solar systems, now you have a switchboard that needs to allow a maximum of 51A (35+16) where it originally was designed for 40A (or so). You would be surprised how many “Professionally” installed PV systems with bad circuits are out there, it all goes well, until it doesn’t…
The next thing, where most residential setups fail, is selectivity. Because, when doing it right (see 2nd paragraph), you have a MCB & RCD combo in front of your inverter and next the MCB & RCD combo’s in your (existing) circuit board. Current selectivity for your MCB’s can easily be found in the provided tables from the manufacturer, or using a more quick & dirty ratio of 1.6 (ie. 40A → 25A → 16A → 10A). There are also different types of MCB’s (like Type B & C) with different characteristics. More advanced designs can have back-up or cascade like implementations based on manufacturer provided coordination tables, but that’s extremely rare in residential circuits.
Selectivity for your RCD’s are even more fun… Assuming everything more than 30mA is fatal for a human, end devices should be protected by a 30mA RCD (probably already covered in your main switchboard or perhaps wall socket in the UK). Selecting a RCD in front of your inverter should not only be selective by current (most of the times x3, so for 30mA => 90mA) but ALSO by time, this is different from selecting MCB’s. I’m not aware of 90mA RCD’s, there are some 100mA (=>90mA) out there, but more widely available RCD’s are 300mA (which also are => 90mA). So the only reasonable RCD in a standard residential setup , in front of your inverter, should be a 300mA Selective (current + time) RCD, be aware, these are expensive.
But again, this depends on rules and regulations in your specific region/country.
Although the different setups below will work perfectly from an electrical point of view, these are considered badly designed and/or unsafe residential electrical circuits in general:
- No MCB or RCD in front of inverter
- A 30mA RCD (inverter) in series with another 30mA RCD (switchboard)
- A 300mA non-selective RCD (inverter) in series with an 30mA RCD (switchboard)
Regarding MCB selectivity, one can argue for weeks how practical (and required) it is to be fully selective. As long the implications are known and accepted, be creative. Do NOT play with ground faults, it kills you…
Victron is providing the inverter, any guidance how to connect this device to your local grid & switchboard would end up with >100.000’s of variables. That’s one reason why there’s a network of local Victron Professionals.