The mp’s will provide the rest if you draw more than specified at max amps import with an max system power you set at the maximum inverter power under ESS.
Are you not afraid to blow the main incoming grid fuse that way? Or is main fuse higher than 33A
In NL you have to set mp2 max input current lower than grid current to now blow the incoming grid fuse (only grid company can change that if it blows, with additional costs)
Main fuses are accessible C25A MCB units. More than 10 hours import or export with 21kW does not have much impact.
Only DC combined grid 21kW + PV approx. 20kW will let the DC system get a bit more warm than usual, but around 780amps that’s ok. This is only sometimes the case under ideal sunny circumstances.
Periodic IR camera checks don’t show any heating concerns.