ESP PowerMan Problem
I have a legacy ESP PowerMan AC-CO-110A/PL/3xM controlling three MultiPlus units. Following a shore power interruption and restoration at the marina, the ESP panel now permanently displays 000V and 000A on both shore and generator supplies. Generator indication still works correctly and all charging/inverter functions operate normally. F1 on the PowerMan PCB was found blown and has been replaced, but the fault persists. Are any schematics, repair information, replacement boards or modern compatible alternatives available?
Good evening,
I tried to see/find that power manager, but it looks something self built and I couldn’t get a drawing.
If you have a contact from where it was bought and/or installed that would be your first choice to ask, I found a 230V one built in Turkey…which is probably completely different…
If you can make a photo and try to get the drawing, that would be great, we can then try to get you up and running asap with BETTER Victron stuff instead that esp, so you never have that issue again…
Regards, Jeroen.
It’s a victron unit, supplied by Energy Solutions; I think its actually the 64A version; there are controllers for shore; generator; multi 1; multi 2; multi 3. They all still work; fuse F1 has blown and getting no readings on the ESP System Control Panel
Good evening,
Aaaah, I thought an esp, but actually it IS an ESP panel, well, these are faded out since 2007-isch.
I cannot come for that, simply to expensive for what it is, it’s by all means almost impossible to repair as it has the VE-net display as well probably, isn’t it?, go to your local electrician first and ask him if he can find/pin point that short circuit on the PCB first, it’s most probably the IC which gets the CT current and also the voltage only, if not…then you have to consider an upgrade to a Cerbo GX.
Ask your local Victron dealer/installer for a solution and a proposal.
When in dock, did they do some welding, and they didn’t put an earth wire, and didn’t take the minus off the batteries, for sure…we see it all the time…
Regards, Jeroen.
Good evening again,
Checking more your photo, we discovered that R1 might be the issue, send an e-mail to tour local Victron contact, with this photo, ask the resistance value in Ohms of that R1 resistor and let your local electrician solder a “bigger” one on it (space enough).
If a better photo of that resistor, it might be possible to see the colours/stripes on it…
It looks like an 1/4Watt one, so, solder a 1/2W or 1W on it, that will outlast the current and “burn” then the item which is faulty, or, maybe it is this resistor, simply not having resistance (open loop) anymore ..
Regards, Jeroen.
Thanks Jeroen - are you able to confirm the fuse ratings for F1, 2 and 3 : the blown one i removed from F1 was a 1A fast blow, but the panel has ‘All fuse 200mA 250V’ clearly written on it. When I’m back at the boat will get a better picture and post
Good afternoon,
Yes, all fuses 3 are 200mA, see attached brochure and manual from that time.
Brochure_ESPSystemsAndPanels_11-07_EN.pdf (2.0 MB)
Regards, Jeroen.