# Error #67 on MPPT RS 450/200 after BMS control already disabled

**URL:** <https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660>\
**Category:** DIY\
**Tags:** mppt, ekrano\_gx, mppt\_controllers, victronconnect, multiplus-ii, diy, cerbo-gx\
**Created:** [9 September 2026 19:26 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660 "2026-09-09T19:26:02Z")\
**Posts on this page:** 15\
**Page:** 1

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [9 September 2026 19:26 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/1 "2026-09-09T19:26:02Z")

</div>

Has anyone got an MPPT RS running without a BMS? I’ve got a three-phase setup: 3x MultiPlus-II 48/10000 on an Ekrano, MPPT RS 450/200, and a Docan bank with CAN BMS, all on VE.Can.

When I wanted to take the BMS out I first set BMS control to “no BMS” on the Ekrano, then disabled BMS control in the MPPT via VictronConnect as well. Looked fine, but as soon as the BMS was actually disconnected I still got error 67 and the whole system went down. Plug the BMS back in and everything runs again, every time.

Does the MPPT need a full factory reset, or is it picking up from VE.Can that a BMS should be there? And why do the Multis go down too when it’s only the MPPT throwing an error?

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [9 September 2026 19:26 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/2 "2026-09-09T19:26:04Z")

</div>



---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [9 September 2026 20:52 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/3 "2026-09-09T20:52:19Z")

</div>



---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [10 September 2026 05:21 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/4 "2026-09-10T05:21:42Z")

</div>

I have done something similar with varied results.

Sometimes there are no issues and there is no control as you want, but other times we get the error. I think the difference is how the BMS interaction is done.

Since yours is not on the official list unexpected behaviours like these, should be expected. One system had to have DVCC completely off.

The error 67 is a system wide one, so will affect everything.

---

<div class="post-metadata">

**Author:** ![alexpescaru](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alexpescaru/32/270_2.png) [@alexpescaru](https://community.victronenergy.com/u/alexpescaru)\
**Post date:** [10 September 2026 08:34 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/5 "2026-09-10T08:34:32Z")

</div>

> [@Araaf](#):
>
> When I wanted to take the BMS out I first set BMS control to “no BMS” on the Ekrano, then disabled BMS control in the MPPT via VictronConnect as well.

Did you also performed the Reset function in the BMS Control section?

 ![1](https://europe1.discourse-cdn.com/victron/original/3X/5/3/538bdc88affed1d06f8c29cf1fdd62e7f2ba8e39.jpeg)  
 ![2](https://europe1.discourse-cdn.com/victron/original/3X/1/f/1f4c8cf295ad862260402d454293cd8599673836.jpeg)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [10 September 2026 09:10 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/6 "2026-09-10T09:10:41Z")

</div>

To switch from managed to unmanaged needs the devices to all be power cycled. It isn’t dynamic.

---

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [10 September 2026 12:14 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/7 "2026-09-10T12:14:29Z")

</div>

Thanks. So the Multiplussen need to be cycled as well?

---

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [10 September 2026 12:15 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/8 "2026-09-10T12:15:00Z")

</div>

Yes, this is how I did it. Sorry, didn’t describe it accurately.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [10 September 2026 17:35 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/9 "2026-09-10T17:35:11Z")

</div>

Correct they do need to be power cycled after BMS is removed in dvcc

---

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [21 September 2026 18:41 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/10 "2026-09-21T18:41:29Z")

</div>

Hi all, power cycling didn’t solve it. After setting BMS control to none on the Ekrano, disabling it in the MPPT and power cycling everything, the Multis still throw a low battery alarm and stop charging. Battery is fine at that point, 53.4V and 77% SOC, BMS cable still connected, and the GX logs BMS lost. In island mode that alarm takes the whole system down. Setting BMS control back to the battery clears it instantly, no restart needed. Is ESS on lithium just not meant to run without GX BMS control?

---

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [21 September 2026 18:54 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/11 "2026-09-21T18:54:48Z")

</div>

Thanks. I didn’t respond to your answer earlier, because I didn’t know what to make of it, but now it seems to make sense. On the system where DVCC had to go off completely, did ESS keep working normally? And how did you handle charge limits then, just the absorption and float settings in the Multis and MPPT?

My batteries have a BMS and contactor per module, so I’m a bit worried that without DVCC the first thing to stop an overcharge is a contactor opening under load. But I am seriously considering turning off DVCC and managing everything through Node-RED.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [22 September 2026 10:57 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/12 "2026-09-22T10:57:51Z")

</div>

> [@Araaf](#):
>
> Multis still throw a low battery alarm and stop charging

When you remove BMS control, everything has to be restarted. Even the inverter. It is a system wide change. Every component is affected.

Ess works normally without BMS control.

> [@Araaf](#):
>
> And how did you handle charge limits then, just the absorption and float settings in the Multis and MPPT?

Properly programmed everything works well. I have quite a few times run smart batteries dumb this way.

> [@Araaf](#):
>
> and managing everything through Node-RED.

I have on one system (because the BMS firmware and control is plain stupid) made a virtual battery set that as the default battery in Dvcc - that uses some information from the actual BMS (like the all important high and low cells) and controls the system that way.

---

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [22 September 2026 12:54 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/13 "2026-09-22T12:54:24Z")

</div>

Yes, I did restart everything, but it seems at least the Multiplusses are still expecting a BMS and throw a low battery alert. My next test will be turning off DVCC entirely.

> [@lxonline](#):
>
> I have on one system (because the BMS firmware and control is plain stupid) made a virtual battery set that as the default battery in Dvcc - that uses some information from the actual BMS (like the all important high and low cells) and controls the system that way.

Wow, making a virtual battery sounds very complicated! How did you go about doing it? Did you need to plug in a cable to simulate a BMS-signal? What external hardware was required? Or could you do it with all software?

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [22 September 2026 17:01 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/14 "2026-09-22T17:01:36Z")

</div>

No external hardware. The BMS is still connected to the GX but it’s not the controlling device.

> [@Araaf](#):
>
> DVCC and managing everything through Node-RED.

The virtual battery is created in Node Red. Which you were already talking about

---

<div class="post-metadata">

**Author:** ![Araaf](https://avatars.discourse-cdn.com/v4/letter/a/3bc359/32.png) [@Araaf](https://community.victronenergy.com/u/Araaf)\
**Post date:** [30 September 2026 10:59 UTC](https://community.victronenergy.com/t/error-67-on-mppt-rs-450-200-after-bms-control-already-disabled/62660/15 "2026-09-30T10:59:11Z")

</div>

Ok, I’ve gone with the virtual battery route and things are looking good so far. No glitches or errors. I combined it with the firmware upgrade of the Mutliplusses to the latest version. Fingers crossed that the whole setup will be stable enough from now on.