# Error 11 after setting country code (Grid) on EasySolar-II GX

**URL:** <https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477>\
**Category:** DESS\
**Tags:** vrm, ess\
**Created:** [10 November 2025 16:38 UTC](https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477 "2025-11-10T16:38:10Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![FloHk](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/flohk/32/32096_2.png) [@FloHk](https://community.victronenergy.com/u/FloHk)\
**Post date:** [10 November 2025 16:38 UTC](https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477/1 "2025-11-10T16:38:10Z")

</div>

Hello everyone,

I have an EasySolar-II GX installed in a converted truck. At the moment, I’m parked on a plot of land with access to the grid, but about 1,200 meters away from the main electricity meter (the cable size and distribution panels were designed for this distance).

I wanted to test the ESS assistant without grid feed-in. To do that, I had to enter the country code (Grid), and since then I’ve been getting Error 11 – Grid relay test failed.  
I can no longer connect to the grid.  
It’s impossible to change this parameter again, even after removing the assistant.  
I even tried to restore an old configuration file (.vsc) via VRM, but I keep getting the missing password message.

I really need to remove this setting, especially since I travel between different countries with my vehicle.  
I don’t actually need the assistant — I only wanted to test it to see how it behaved, as I was planning to stay in one place for about six months.

Thanks in advance for your help!  
If anyone has encountered this issue after adding a country code, I’d really appreciate any advice on how to properly disable it.

---

<div class="post-metadata">

**Author:** ![Fideri](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/fideri/32/2275_2.png) [@Fideri](https://community.victronenergy.com/u/Fideri)\
**Post date:** [10 November 2025 17:06 UTC](https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477/2 "2025-11-10T17:06:08Z")

</div>

You can’t get a password from your Victron supplier to change the grid code?

---

<div class="post-metadata">

**Author:** ![FloHk](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/flohk/32/32096_2.png) [@FloHk](https://community.victronenergy.com/u/FloHk)\
**Post date:** [10 November 2025 17:09 UTC](https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477/3 "2025-11-10T17:09:23Z")

</div>

If that’s the only solution, I’ll call them tomorrow, but they’re just resellers, not installers.

---

<div class="post-metadata">

**Author:** ![Fideri](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/fideri/32/2275_2.png) [@Fideri](https://community.victronenergy.com/u/Fideri)\
**Post date:** [12 November 2025 11:52 UTC](https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477/4 "2025-11-12T11:52:42Z")

</div>

I can’t give details but if that fails:

1. Sign up at [professional.victronenergy.com](http://professional.victronenergy.com), watch a video, and get the password.
2. Or cleverly (not here) Google for a password.

Not recommended but sometimes, you must close your eyes and do what must be done. Remember philosophically, if nobody saw anything, you didn’t do it 😜

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [12 November 2025 12:02 UTC](https://community.victronenergy.com/t/error-11-after-setting-country-code-grid-on-easysolar-ii-gx/48477/5 "2025-11-12T12:02:19Z")

</div>

FYI [error 11](https://www.victronenergy.com/live/ve.bus:ve.bus_error_codes#error_11_-_relay_test_fault_-_installation_error_or_possibly_relay_failure) is a wiring fault related code. So something there doesn’t meet code.

But yeah being a in a truck means you don’t meet a grid standard mobile installs are usually done a little differently in terms of grounding and bonding.  
ESS should [not be used in mobile installs.](https://www.victronenergy.com/media/pg/Energy_Storage_System/en/ess-introduction---features.html#UUID-b26ba3e6-708a-268b-66bc-2681a9c4ea78)

> **Summary**
>
> ![IMG_20251112_140144](https://europe1.discourse-cdn.com/victron/original/3X/b/0/b0adfcb467ea0f4969cdb8f811bf9ae131a32476.jpeg)

There is another option that is _[solar wind priority](https://www.victronenergy.com/media/pg/Solar_&_Wind_Priority/en/index-en.html)_.