# Cell balancing

**URL:** <https://community.victronenergy.com/t/equilibrage-des-cellules/61895>\
**Category:** DIY\
**Tags:** beginner, multiplus\
**Created:** [20 August 2026 10:26 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895 "2026-08-20T10:26:02Z")\
**Posts on this page:** 17\
**Page:** 1

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [20 August 2026 10:26 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/1 "2026-08-20T10:26:02Z")

</div>

Hello,

I have an installation consisting of a MultiPlus 48/5000, four 12.8 V/90 Ah batteries connected in series, a CCGX and a SmartSolar MPPT 150/85 VE.Can.

For the past few days, the system has been switching back and forth between Sustain mode and Self-consumption mode at very short intervals (i.e. every minute or two). The consumption (AC-out 1) at that point is around 2,500 W and solar production is low (at the end of the day, 100 to 200 W). Sometimes the CCGX even shuts down and restarts (the BMS cuts out).

I suspect that one or more of the batteries may have unbalanced cells. I have read the procedure for rebalancing them individually using a Blue Smart charger, but I don’t have one.

Is it possible to perform this rebalancing using the MultiPlus? (I can disconnect the Victron system from my electrical installation to do so.)

Many thanks in advance for your replies.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [20 August 2026 10:58 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/2 "2026-08-20T10:58:06Z")

</div>

What batteries are you using?

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [20 August 2026 11:57 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/4 "2026-08-20T11:57:56Z")

</div>

Victron LiFePO4 12.8V/90Ah (not “smart”, so no Bluetooth), purchased in 2017/2018.

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [20 August 2026 12:16 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/5 "2026-08-20T12:16:31Z")

</div>

In my opinion, connecting them in series is always problematic.  
(Although it usually works reasonably well with Victron batteries, since you have a higher-level BMS.)

You should disconnect the system and then measure the voltage of each battery first.  
After that, charging them individually (or in parallel) would be best; that’s the only way to bring them all to the same voltage.  
You won’t be able to balance them properly when they’re connected in series.

It’s important to charge them at a low current, and the BMS must be able to disconnect the charger or charging current.

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [20 August 2026 12:20 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/6 "2026-08-20T12:20:34Z")

</div>

So it needs to be done with a Blue Smart charger. If I understand correctly, the BMS also needs to remain active during balancing. How can the BMS control this charger? I’m using a VE.Bus BMS in my system.

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [20 August 2026 13:18 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/7 "2026-08-20T13:18:59Z")

</div>

Take a look at the BMS manual.  
You need a Cyrix-Li-Charge or a BatteryProtect, or something else to switch off the charger via a signal from the BMS.

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [20 August 2026 13:25 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/8 "2026-08-20T13:25:12Z")

</div>

Since the VE.Bus BMS load-disconnect signal is high (12 V?) during normal operation, can I use a 12 V DC/230 V AC normally open relay to power the Blue Smart charger? If it goes low, the charger will switch off. Is the BMS load-disconnect high state indeed 12 V?

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [20 August 2026 13:40 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/9 "2026-08-20T13:40:36Z")

</div>

Sorry, I think I got it wrong; I believe it’s the charge disconnect that needs to be connected to the relay, right?

If we remove the two RJ45 cables, can we connect the battery negative to Battery - on the BMS?

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [5 September 2026 16:17 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/10 "2026-09-05T16:17:59Z")

</div>

Hello,

I received my Blue Smart Charger and installed the device as follows to rebalance the cells:

On the Ve.bus BMS:  
Battery -: connected to the battery negative terminal  
Charge disconnect: connected to the positive terminal of the coil of a 12 V/230 V contactor  
Battery +: connected to the battery positive terminal  
The RJ45 cables are disconnected from the BMS sockets

The negative terminal of the contactor coil is connected to the battery negative terminal.  
The charger is connected to the battery’s + and - terminals, and its 230 V power supply is connected to the contactor’s 230 V terminals.

The battery voltage is 13.31 V.

When I switch on the BMS, it does not activate the contactor; the voltage across the coil terminals is around 3–4 V.  
Do you know why the Charge disconnect terminal is not in its high state? (The voltage at Load disconnect is 11.5 V.)

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [5 September 2026 16:21 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/11 "2026-09-05T16:21:58Z")

</div>

Have you checked the datasheet / manual for the VE Bus BMS to see if the current rating of the ATC is enough for you contacto.

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [5 September 2026 16:36 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/12 "2026-09-05T16:36:50Z")

</div>

If I measure the open-circuit voltage at the Charge Disconnect terminal, I do indeed get just over 13 V… The VE.bus BMS only supplies 10 mA on this output, so I need to find a contactor that operates with this current. Do you have a part number for such a product?

Thanks, pwfarnell!

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [5 September 2026 19:54 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/13 "2026-09-05T19:54:45Z")

</div>

You need a solid state relay to work from this low current, look at the Victron SolidSwitch 104.

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [6 September 2026 16:03 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/14 "2026-09-06T16:03:47Z")

</div>

Thanks, pwfarnell! That’s exactly what I was looking for!

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [15 September 2026 18:52 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/15 "2026-09-15T18:52:23Z")

</div>

Good evening,

A quick follow-up question: I have received the SolidSwitch 104, but I wanted to check its compatibility with my power contactor.  
If the battery is in absorption mode (14.4 V, so also across the SolidSwitch’s − and + terminals), what will the voltage be between the SolidSwitch’s − and load terminals? My contactor only accepts 1.1 × 12 V, i.e. 13.2 V…

Many thanks in advance for your answers.

---

<div class="post-metadata">

**Author:** ![pwfarnell](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/pwfarnell/32/2341_2.png) [@pwfarnell](https://community.victronenergy.com/u/pwfarnell)\
**Post date:** [15 September 2026 19:46 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/16 "2026-09-15T19:46:51Z")

</div>

I do not know the internal components but expect the switching to use a FET which will have a low resistance and pass full battery voltage to the load.

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [15 September 2026 20:08 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/17 "2026-09-15T20:08:06Z")

</div>

Okay, thanks, I’ll look for a suitable contactor.

---

<div class="post-metadata">

**Author:** ![GreenGimmick](https://avatars.discourse-cdn.com/v4/letter/g/ecae2f/32.png) [@GreenGimmick](https://community.victronenergy.com/u/GreenGimmick)\
**Post date:** [3 October 2026 12:31 UTC](https://community.victronenergy.com/t/equilibrage-des-cellules/61895/18 "2026-10-03T12:31:56Z")

</div>

Hello, I found a suitable contactor and started the balancing process. However, I’m wondering what conditions need to be met before the cells can be considered balanced. I left the batteries on absorption at 14.2 V for several hours. The current supplied by the charger was quite low, between 0 and 0.5 A. If I disconnect the battery, it then reads around 14.18–14.2 V at the terminals. A few hours later, about 8 to 10 hours, the voltage is down to just 13.75–13.77 V. Can the balancing still be considered complete?