# Enphase-Cerbo GX communication problem due to fake PV instance in list

**URL:** <https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911>\
**Category:** DIY\
**Tags:** enphase, solar\_panel, dess, vrm, cerbo\_gx, ess, cerbo-gx\
**Created:** [25 July 2026 21:08 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911 "2026-07-25T21:08:07Z")\
**Posts on this page:** 7\
**Page:** 1

<div class="post-metadata">

**Author:** ![hkiela](https://avatars.discourse-cdn.com/v4/letter/h/b782af/32.png) [@hkiela](https://community.victronenergy.com/u/hkiela)\
**Post date:** [25 July 2026 21:08 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/1 "2026-07-25T21:08:08Z")

</div>

I have found a problem in the communication between Cerbo GX and the Enphase PV system.

Initially the communication was configured in the Remote console and via a request to Enphase activated in the Envoy local host of the Enphase system. All worked fine for some month and then suddenly the PV system disappeared from the VRM page and in device Victron reported that it had not seen the PV system for some time.

In the Remote console the connection was established via the manual IP address as Victron was unable to locate the Envoy via the search.

Before the last reset by Enphase, I did re-install a new firmware 3.74 in the Cerbo GX initially hoping for a restore of the PV system in VRM, wich didn’t work.

So I contacted Enphase again and they were able to revive the connection again. It worked for some weeks and then the same happened (Disappeared PV system from VRM and error in devices list)

I again contacted Enphase a few days ago. They spent quite some time on it from thier side in the Enphase system. They could see that the modbus connection from Victron to Envoy was made, but the communictaion did not start.

In the mean time I noticed that Victr has changed things in the PV device area.

I now suddenly see two devices. One with serial — at the top row and on the second row the serial of the real Enphase system.

This i have not seen before. Must have been introduced in the 3.74 firmware.

So I now get the feeling that the first PV device with serial — is now interfering and blocking the true modbus connecton to the PV installation.

But there is no way unfortunately to delete the first or both entries en re-initialize the connection.

So my request is:

How to remove/clean up the PV devices to allow the true PV installion appear in the VRM. This connection is a necessity for proper DESS planning.

As a result I cannot use DESS now for quite some weeks which makes the Victron system useless for this aspect.

Any suggestions and help is appreciated

---

<div class="post-metadata">

**Author:** ![hkiela](https://avatars.discourse-cdn.com/v4/letter/h/b782af/32.png) [@hkiela](https://community.victronenergy.com/u/hkiela)\
**Post date:** [25 July 2026 21:10 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/2 "2026-07-25T21:10:12Z")

</div>

Added the screenprint of the two instances in remote console

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/b/d/bd114a57458415815a45ba8bd5e15187eb3a43c8.png)

---

<div class="post-metadata">

**Author:** ![hkiela](https://avatars.discourse-cdn.com/v4/letter/h/b782af/32.png) [@hkiela](https://community.victronenergy.com/u/hkiela)\
**Post date:** [25 July 2026 21:11 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/3 "2026-07-25T21:11:13Z")

</div>

I toggled the display switch for both instance independently without any effect in the visibility in VRM

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [26 July 2026 17:01 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/4 "2026-07-26T17:01:20Z")

</div>

There have been other posts and enphase had been engaged by individual users, somthing about a firmware update from enphase that has been messing with the modbus.

> [@Enphase modbus system not showed in VRM](https://community.victronenergy.com/t/enphase-modbus-system-not-showed-in-vrm/58535):
>
> It happened again, mine Enphase system doesn’t show up in VRM. A re-scan of the PV inverters did help last time, but doesn’t seem to help this time. Is there a way to check if Enphase did turned off modbus support? Anyone noticed the same issue?

---

<div class="post-metadata">

**Author:** ![hkiela](https://avatars.discourse-cdn.com/v4/letter/h/b782af/32.png) [@hkiela](https://community.victronenergy.com/u/hkiela)\
**Post date:** [26 July 2026 18:43 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/5 "2026-07-26T18:43:38Z")

</div>

Thanks for your reaction.

You are right about the other topic. I have read it now from bottom to top. All kind of Enphase modbus relatedthings. But no one report a double entry in the Remote console of Victron.

So my question remains how to get rid of both entries from Victron to rescan or manually enter the Enphase IP address in the expectation that it will work now

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [26 July 2026 19:49 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/6 "2026-07-26T19:49:58Z")

</div>

Yeah.

> [@hkiela](#):
>
> hoping for a restore of the PV system in VRM, wich didn’t work.

> [@hkiela](#):
>
> Disappeared PV system from VRM and error in devices list)

Yeah i was addressing this issue.

> [@hkiela](#):
>
> now interfering and blocking the true modbus connecton to the PV installation

The duplicate device i have no idea.

For the most part then a GX reset would probably be the way. It means setting uo your settings there again

---

<div class="post-metadata">

**Author:** ![hkiela](https://avatars.discourse-cdn.com/v4/letter/h/b782af/32.png) [@hkiela](https://community.victronenergy.com/u/hkiela)\
**Post date:** [26 July 2026 20:57 UTC](https://community.victronenergy.com/t/enphase-cerbo-gx-communication-problem-due-to-fake-pv-instance-in-list/60911/7 "2026-07-26T20:57:10Z")

</div>

Does not sound logic to me.

Resetting the Victron system (Cerbo GX or MP2’s as well?) and configuring again is a lot of work.

And for how long would this last if the cause for the double is unknown?

The firmware update of today to 3.75 did not have any effect.

How can I remove the two entries from the Cerbo GX?