I want to set up synchronised charging in accordance with 4.4.2 of the IP43 Smart Charger Manual using a 12/30 charger and a 12/50 charger using a VE.Direct network. I cannot find an answer to the following point: Is it okay to wire two IP43 L/H terminals to the EkranoGX’s Relay 1 ND and Com, or should I isolate them by using an interposing relay with two separate, normally open contacts—one contact across the 12/30’s L/H terminals and the other across the 12/50’s L/H terminals?
from the manual:
4.11. Remote on/off
There are three ways to switch on the device:
1. Short the L and H pins (factory default)
2. Pull the H pin to a high level (e.g. the battery plus)
3. Pull the L pin to a low level (e.g. the battery minus)
not sure if 1 will work fot 2 chargers parallel, but 2 and 3 should work
Mixing a bt smart network mentioned in 4.4.2 and a GX like the Ekrano never works well. And they are not designed to work together.
Leave the smart BT network out of the equation and leave the Ekrano to be the network device through DVCC. (See point 2 in limitations)
Is there a reason why you want to switch them on/ off via remote?
Thank you for taking the time to respond.
I do not know what a bt smart network is. I am using the Ekrano to monitor the system. Currently I have the IP43 12/30 connected through its VE.Direct port and Relay 1 on the Ekrano is being used to short the L and H pins when applying the conditions in the Genset device. Effectively treating the IP43 as a generator.
Now, I want to add an additional IP43 charger (12/50) to work in unison with the IP43 12/30. I will hard wire the new charger to the Ekrano through a VE.Direct interface. Should I wire the L and H pins on the new charger by doubling up with the IP43 12/30 connections into the Ekrano’s Relay 1. This seems the logical thing to do, but I am unsure if that is what is intended.
Good evening,
It’s never so good to connect h-l together with another one h-l, if one unit fails then it might fail the other one as well.
Also there is always a so slightly different voltage between them…
So, my advise is to use the relay you have in mind and keep the 2 seperate.
Regards, Jeroen.
Neat.
The factory loop can be extended to use the remote like that with the Ekrano relay.
From the manual linked above…
Interconnect / short the L and H terminals (factory default is a shorting link between L and H). The L and H terminal can be interconnected /shorted via a switch, relay or other external device
So yes it can be used like that since basically you are extending the factory loop.
for what reason?
Logical high is high, low is low
Good evening,
Both modules have their own power supply, which can differ of eachother, measure it between h and l and you will see yourself what voltage is there.
So, use a relay with 2 contacts, in that way both are separated, we call it fail save…
Regards, Jeroen.
Thank you for your advice. I will look for a suitable relay with two contacts.