Dynamic ESS not working as before

The Dynamic ESS always runs latest Beta firmware.
One year ago was some problem with RUiXU batteries fixed fast then worked great to somwhere to december 2024 then it works worse and worse now last update 3.60~25 the batterie newer charge from grid or AC cuppled PV inverter only from PV Charger.
No restrictions att all.

Does it need an Energymeter on input now or what changed last months?

Have you been updating the rest of the system along with the gX firmware?

MP2 v555 and what more need update?

I have no idea what else is in the system.
Is the BMS connected to the GX?

Yes RUiXU batteries connected to Cerbo GX

See if there is any information from the battery that is preventing the charge such as CCL or voltage control.
Maybe there is a cell high problem?
Just guesses here.

If none of these things are a problem, try without the battery controlling the system in DVCC.

1 Like

You may say something here look pictures.
BMS report cell high low 0,01v
But never show 0A discharge ?


I have only seen that on batteries where the max current is already being draw and they are about to shut the system down

A cell has failed or bms is not reading one.

The strange thing its just wirh some firmware this problem come,

Upgrade RUiXU battery firmware from V0.7 - > V1.8

Great that they enable you to do that.