DESS using battery instead of grid during low price

Today dess decided to power the house from battery while using grid is cheaper. Why is this happening?

The most exciting little chart (the one at the bottom) is missing…

True, here it is. A few quarters of battery to consumption during the low tarrif followed by charging again from grid, very strange.

It almost seems like it expected more sun so grid setpoint was 0 watts but because there was less sun the setpoint of 0 watt causes energy usage which make no sense.

That is something I never quite understood. The Multiplus is about 75% efficient (round trip) in my case. Why would it ever want to cover consumption and directly charge it back? But if I have to guess, it’s a limitation of DESS committing to a plan and dealing with unexpected loads (or less solar). Sorry, I don’t have the answer, but this is my two cents.

By the way, have you got your prices set correctly? Your buy price is lower than your sell price. Something tells me that can’t be right. My theory is that there was more sunshine at 12:00 than expected, so your battery’s SoC prediction was too high. I’ve noticed that the thing follows the plan fairly rigidly, and that the predicted SoC is what drives it. Corrections don’t always come very quickly, but they do come.

The price is right, I get a 10% bonus from sunrise till sunset and currently I don’t have to pay tax and vat.

Today again the same strange behaviour.

The mode is trade v3.85

It seems dess tries to keep the grid at zero while it should charge from excess solar but use grid for the loads instead of battery

It gets even weirder and worse

I looked at your system, including the debug log for 31 Oct. There are two things going on. On 31 Oct the GX briefly followed an older plan at 12:00, so the battery covered the house until the updated plan arrived 11 minutes later and charged it back. On 29 Oct and 3 Nov the plan expected solar surplus, so the battery covered an unexpectedly large load. Your settings seem fine and I am raising both with the VRM team.

Two questions: do any of your Node-RED flows control ESS and can you confirm the VRM id 701774 (from the url on vrm)?

The vrm id is correct. I also see this at other sites but less dramatic.

I don’t manipulate dess with nodered. The only thing nodered does is lowering dess power setting at night due to the noise of the multiplus and adapting sunset and sunrise times in the dess price schedule because of the zonneplan solarbonus. But that’s just one time a day around 2am.

I think the battery shouldn’t power the loads when the price is low and solar is less than expected. Only when solar is sufficient and the buy price is more expensive than the sell price (minus battery cost and losses) it should use the battery.