Dess is switched off, but Dess is loading anyway

So, due to the lack of sun, the high electric prices ànd the fact that the victron wants to balance again (while it shouldn’t, did that a, week ago, it’s set at once in 2 weeks) we switched off Dess. Also, put soc to 10%. But this morning, it was loading from the net (already at 13 %now). Ofcourse, at the most expensive time of the morning. Why is it doing this?

How did the battery state of charge get so low?

Because I set it to 10%? Because the purchase prices are so high that, including losses, charging is more expensive than drawing power from the grid?

Because it’s just cloudy?

Could it be that your minimum SoC is set too low, or that the SoC itself is incorrect? This causes the battery voltage to drop below the set limit, so the system charges the batteries to prevent them from being damaged.

Tell us more about your system. Green mode or Trade mode? What is the minimum state of charge allowed by your batteries? Can you show some more history?

I have the similar problem with latest beta (3.90 beta 9). It is reported bug. Maybe you have the same firmware?

I’ve been running the whole thing for over 3 years now. Based on my experience, I can say that the calculated SoC isn’t right, and that’s why the minimum voltage was undershot.

The problem often occurs in winter if the system isn’t calibrated regularly, via the shunt or BMS. All the equipment in the battery (BMS, balancer, possibly display …) has a standby power consumption that isn’t taken into account. The shunt or BMS doesn’t detect any consumption, and the SoC slowly drops. So it isn’t at 14–15% or 10%, as calculated in the example, but lower. That’s exactly when the calculated amount of power isn’t enough, or the voltage drops so far that the ESS!!! doesn’t even charge the DESS. Which is also the right thing to do to protect the battery from damage.

I’ve had this problem for years, across all software versions. The only things that help are regular calibration, manually correcting the SoC, or setting a slightly lower efficiency in the SoC.

One solution would be for Victron to account for this standby power consumption in the shunt or when measuring current in some other way.

Yes, I definitely think that’s part of the problem.

But there may be something else going on too. One of the batteries (basengreen) is showing a much lower SOC than the others. For example, earlier today it was at 13% (I charged the system to 25%), while the other three were at 25% or 26%.

I’ve reported this to the installer several times and asked whether that one battery is working properly. The only thing I keep hearing is that SOC doesn’t mean anything and that you have to balance them every week. And if you don’t, the warranty is void.

Now, I’m not planning to rebalance every week under these conditions (very high prices).

You say to correct the SOC manually, calibrate, etc. How do I do that?

To answer this question - the DESS charts will continue to load / refresh if you toggle it off via the side panel. However, the system won’t follow the DESS plan. In your case, the “grid to battery” is historical, meaning your system did charge for some reason but it wasn’t DESS that triggered it.

Well…I know from experience that my batteries have a standby consumption of around 0.5%. I also have a rough idea of which SOC corresponds to each open-circuit voltage. I use VictronConnect to access the shunt and correct the SOC.

I’ve never done a full charge outside the normal schedule. That’s also because of the prices. But apart from calibration, my balancers work differently from the mainstream too. I balance in the upper and lower SOC ranges.

Where do your SOC readings for the individual blocks come from? From the respective BMS units? Then you can forget those readings straight away.

That’s a good question. I basically can’t see the batteries themselves. The installer apparently doesn’t think that’s necessary. I did discover an app, though, where I can see various things for each battery via Wi-Fi.

But how I can calibrate that… no idea. Not yet, anyway :sweat_smile:

I’m a tradesperson, but electrical engineering is completely outside my field. Exactly what you describe has always been the main reason I’ve built most of my system myself. I researched the topic thoroughly and only then built and set up the system. This isn’t meant as criticism of you, but as confirmation that I made the right choice.

We were led to believe quite different things as part of the sales pitch: that the system has a mode that prioritises household consumption and only uses the surplus for trading when it’s profitable. But when I see that the system doesn’t even remember the average value per kWh over several days… I was able to set that up quite easily in Home Assistant.

I don’t know anything about this at all! I’m good with computers… That’s all.

Well, with DESS, there’s no need to keep track of the value or price in that way. The system uses a different, forward-looking approach. It always looks for the cheapest/most economical option over the period covered by the forecasts. Past prices don’t play a role.

Which mode (Green /Trade) is the system set to?

The Buy and Sell formula (DESS setting) is important for DESS to function properly.

At https://vrm.victronenergy.com/ I can find a lot of old data/values.

And under the “Advanced” tab you can find more technical data (Widgets must be installed). You can export this data to your computer (Excel).

Or do you not have access to it?

Not historical prices, though. But in my opinion, the value of the kWh charged earlier should be included. It seems to me that it should use a weighted average.

I’ve added 18% on top of the purchase prices. And for the selling prices, in anticipation of the end of net metering and the fact that I’ve already fed more back into the grid than I’ve taken from it, I’ve set them to the net price plus VAT. This prevents the system from trading at a loss.

It’s now set to trade, and with these settings it works reasonably well.

Though I think the balancing makes no sense at all. It doesn’t take anything into account, charges at the most expensive time of day and then dumps the energy again.

That’s a completely different approach. Which approach is better is something we could argue and debate.
The DESS approach is more flexible and dynamic. It optimises the most economical option every hour. Since the balance between PV generation and consumption is constantly changing, I think this is also a better approach than looking at past purchase prices, whether weighted or not. What good does it do for the system to remember its price? What if it bought electricity “too expensively”? Is it then supposed to keep searching for electricity until it eventually becomes even more expensive?

I’ve been running DESS for 3 years now, and it took me some time to understand the system behind it. By now, I’m convinced by it. What I think would be helpful is a longer forecasting period. PV forecasts and consumption forecasts are already available. There were some attempts at price forecasting, which I found very helpful.