Hi,
I’m working on an off grid system for a cabin. I have a 10KW solar array connected via a RS 450|200. I have a Cerbo running Node Red.
The cabin has hydronic heat with a buffer tank housing six 48V DC, 2,000W heating elements. I’d like to run these using the opportunity loads feature, staging them on in steps. Obviously, I have more heating elements than solar/charger power, so for now I’ll only have four in play. The other two are spares if I ever expand the solar (unlikely).
The heating system is controlled by a custom control panel that has DC solid state relays to control the heating elements . This is operated by a PLC that itself has a Node Red module (Automation Direct CLICK). It also controls the balance of the heating system (backup mod-con propane boiler, circulators, zone valves, outdoor reset, etc.)
What would be the best / most reliable system architecture to bring this all together and pass data between the Cerbo and PLC? Modbus, MQQT, other? My understanding is that the Cerbo is resource limited, so perhaps offloading processing to the PLCs dedicated Node Red module makes sense?
I could add current measurement hardware to the PLC to measure the heater output, but being DC, I assume reporting by simple ohms law calculation would be close enough? I was not planning on modulating the heater SSRs, I was just going to turn on each element 100%, giving me 0, 2KW, 4KW, 6KW and 8KW steps.
Thoughts?
Thank you!