Follow-up to two closed threads:
- Wrong Fronius Modbus value interpretation - v3.80~39
- Dbus-fronius: DC-Werte je MPPT (Pv/x/V, Pv/x/P) um Faktor 10 falsch
In the first one it was confirmed (4 Sep 2026) that the fix for stale SunSpec
scale factors is in the dbus-fronius master branch, but too late for v3.80.
I see the same issue on a Fronius Symo 4.5-3-M (two trackers, 2 × 3045 Wp),
Cerbo GX, Venus OS v3.80, SunSpec via Modbus TCP. Per-tracker DC power
(/Pv/0/P, /Pv/1/P) is ~10x too high at low irradiance, while /Ac/Power is
correct and matches Solar.web.
Energy per 15-min slot on 2026-10-16:
slot PV0 + PV1 (DC) AC ratio
15:00 292 Wh 271 Wh 1.1 (OK)
15:30 621 Wh 55 Wh 11x
15:45 454 Wh 38 Wh 12x
16:00 430 Wh 35 Wh 12x
Peak tracker 2 reading: 6539 W at 15:29, on a 3045 Wp string.
Which Venus OS release will include the fix? I am happy to test a beta.