Hello again. I have my Quattro limited to draw max 10 amps from the grid (it’s actually a secret cable to my other house, as technically, we’re off grid). This morning I saw it drawing 5kW. That’s almost enough to trip out the supply. 23 amps!. Is this a known bug? Is there a workaround? My house is a bit like a boat - off grid but with external power available when necessary.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [4 January 2025 17:49 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/3 "2025-01-04T17:49:41Z")

</div>

Thanks. I’m on 506.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [5 January 2025 11:40 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/5 "2025-01-05T11:40:17Z")

</div>

OK. Done that. The “charge to 100%” still doesn’t work. We’ll see if the current gets exceeded next time the batteries drop to the limit and we connect to the grid. I’ve seen it mentioned that I should disable power assist. Is this right? And if so, how? I don’t see the option in Victron Connect.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [5 January 2025 12:00 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/7 "2025-01-05T12:00:08Z")

</div>

The option to charge batteries to 100% from grid and then switch back to solar priority. Perhaps it’s designed not to work if we have limits set?

 ![Captura de pantalla de 2025-01-05 14-48-49](https://europe1.discourse-cdn.com/victron/original/2X/0/0e1df52f720eb945bdcc0e3b7132c30e2000842f.png)

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [5 January 2025 14:21 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/8 "2025-01-05T14:21:04Z")

</div>

There are a few settings that affect this.  
ESS if you are using it.  
The other is power assist and if you have weak ac enabled.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [5 January 2025 14:35 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/9 "2025-01-05T14:35:10Z")

</div>

Thanks. I don’t have ESS as I’m strictly speaking off grid. I think I may have weak AC enabled, but may have to confirm that. I don’t know where to find power assist.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [5 January 2025 14:43 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/10 "2025-01-05T14:43:38Z")

</div>

Ok. It looks like you have [solar wind priority](https://www.victronenergy.com/media/pg/Solar_&_Wind_Priority/en/introduction.html)?

[Power assist is here](https://www.victronenergy.com/media/pg/VEConfigure_Manual/en/inverter-settings.html#UUID-0991f1c4-c5c8-61f6-ba31-22d218f0e04e).ve config

Or [victron connect](https://www.victronenergy.com/media/pg/VictronConnect_configuration_guide_for_VE.Bus_products/en/description-of-settings.html#UUID-cb8538f0-f216-08b6-cd38-e89f7b649e5b).

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [5 January 2025 15:37 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/11 "2025-01-05T15:37:01Z")

</div>

BTW, I feel I should mention that the upgrade was painless. All done from a combination of 2 PCs on my home network (1 windows and 1 linux) remotely. Included a couple of power outages and each time the browser recovered and carried on. Very surprised. I was expecting a nightmare.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [6 January 2025 15:51 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/12 "2025-01-06T15:51:34Z")

</div>

It’s looking like with PA enabled all bets are off. I’ll disable it when the pellet fire is off (can’t risk outage with it on - it takes an age to get going again).

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [6 January 2025 16:11 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/13 "2025-01-06T16:11:46Z")

</div>

Yeah there has been some hard work hard on making it more user friendly.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [6 January 2025 16:12 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/14 "2025-01-06T16:12:15Z")

</div>

You shouldn’t get a power outage with power assist. Are your batteries able to supply full current for your loads? What size system vs load are you running?

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [6 January 2025 16:35 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/15 "2025-01-06T16:35:30Z")

</div>

Sorry, I didn’t explain myself. Sometimes connecting the mk3 to the Quattro will make the system shut down (if I make changes). If I disconnect the CCGX (which several people have told me I should) it thinks the batteries are flat and shuts down.

We go the whole year without help from the grid - well, apart from a few times around this time of year. We are in Andalusia where the sun shines a lot.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [6 January 2025 16:57 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/16 "2025-01-06T16:57:52Z")

</div>

Ah yes. If you dally around it does that 😆.  
Not realy fun.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [6 January 2025 17:42 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/18 "2025-01-06T17:42:52Z")

</div>

Pylontech with their BMS. So no.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [7 January 2025 11:31 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/20 "2025-01-07T11:31:02Z")

</div>

Just went to disable PA and it isn’t even enabled. So why else can the system be drawing so much from the grid? BTW, I disabled weird frequency tolerance.

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [7 January 2025 14:44 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/21 "2025-01-07T14:44:16Z")

</div>

I noticed that when we are drawing high currents, the CCGX says we’re in passthrough mode. I’ll investigate this, but if anyone here can elighten me…

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [7 January 2025 15:02 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/22 "2025-01-07T15:02:03Z")

</div>

OK. I’ve read a bit. It looks like I should have PA enabled. Currently when it flicks over to grid (18% battery), the house runs from grid - batteries stay the same. When sun comes up, batteries start charging from solar. If PA not enabled and demand increases, we hit the grid for lots of amps. If I enable PA, this should allow the batteries to assist with the high demand until it drops off, when solar goes back to the charging. This also means that at night time, all the grid does is feed the nocturnal loads. Am I on the right track? So the grid never charges the batteries?

---

<div class="post-metadata">

**Author:** ![paulcarmichael](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/paulcarmichael/32/2532_2.png) [@paulcarmichael](https://community.victronenergy.com/u/paulcarmichael)\
**Post date:** [20 January 2025 16:11 UTC](https://community.victronenergy.com/t/current-limits-exceeded-by-a-lot/17501/24 "2025-01-20T16:11:00Z")

</div>

Enabled PA and problem gone away. Just have to keep an eye on battery level (assuming I can trust the BMS for this). It’s rained all day today and the batteries are at 40% and we’re drawing 2k from the grid. I think it’s set to drop the grid at 50.5V, which won’t happen for a while with no sun.