# Critical loads causing excess export when setting modbus register 37

**URL:** <https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111>\
**Category:** Modifications\
**Tags:** modbus\_tcp, vrm, multiplus-ii, ess\
**Created:** [31 December 2024 16:46 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111 "2024-12-31T16:46:53Z")\
**Posts on this page:** 19\
**Page:** 1

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [31 December 2024 16:46 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/1 "2024-12-31T16:46:54Z")

</div>

I am sending -500w to modbus regster 37 on unitid 228 (VE.Bus)  
To feed back 500w to the grid.

I am also reading back the value from modbus to ensure I had written it correctly, no issue here.  
I am reading what I am writing.

But in actuality I am getting ± 857w feed back to the grid.  
I dont understand why, when checking the VRM I can see Critical Loads being added to the grid feedback?

Can I disable the critical loads import ? I have connected the wiring up to AC OUT 1.  
And ofcourse AC IN.

VRM :

 ![-500](https://europe1.discourse-cdn.com/victron/original/2X/3/3385385555bbc70943005192e59291623a9e8653.png)

Readings :

 ![image](https://europe1.discourse-cdn.com/victron/original/2X/8/81f6ba1abac1c239e1eb3a6d24b2adef09e8d4af.jpeg)

Thanks for any insights/help.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [31 December 2024 18:46 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/2 "2024-12-31T18:46:07Z")

</div>

Help me understand here.

1. You have a load ln the inverter output
2. . You are discharging from battery to grid (target 500W)
3. You don’t want the battery to discharge to the load- where do you want the power to come from for the load?

The target to grid is being met (shy of a few watts).

What is being discharged from the battery is load + grid is how i understand your vrm upload.

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [31 December 2024 21:08 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/3 "2024-12-31T21:08:04Z")

</div>

Hi LX,

I would expect if I send -500 that I would get approximately -500 feedback to the grid.  
I dont understand why this “Critical Load” is also added ontop of the feedback, generating a surplus on the requested feedback.

I would be very happy if only the left side was fed back (-480).

Any ideas how to improve or how other people deal with this ?

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [31 December 2024 22:44 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/4 "2024-12-31T22:44:02Z")

</div>

Its called critical loads for a reason, so that means it always have to have power…

System is functioning as it should, supply power to critical loads and still keep your grid at setpoint…

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [1 January 2025 05:40 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/5 "2025-01-01T05:40:07Z")

</div>

They have their grid set point at 0w and allow battery discharge.

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [1 January 2025 11:50 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/6 "2025-01-01T11:50:12Z")

</div>

1. Is there anyway to disable the critical loads ?
2. Is there some calculation behind it ? What is the logic here ?

I am still not understanding why if I say -500, it will trigger the critical loads also.  
Here are some more examples

Value : -100, no effect, works as expected, I am feeding back to my grid 84w

 ![-100](https://europe1.discourse-cdn.com/victron/original/2X/b/bcf7982a446854fa0309bc60d359e5c241334060.png)

Value : -200, adds 296w of Critical Loads, I am feeding back to my grid 502w

 ![-200](https://europe1.discourse-cdn.com/victron/original/2X/3/33189dff96cc196cbd0e8d663bf44725bac62b8a.png)

Value : -500, adds 377w of Critical Loads, I am feeding back to my grid 857

 ![-500](https://europe1.discourse-cdn.com/victron/original/2X/3/3385385555bbc70943005192e59291623a9e8653.png)

Then when I request the battery to charge, there is also a surplus of power draw.

Value : 100, getting 147, still acceptable for me in a way.

 ![100](https://europe1.discourse-cdn.com/victron/original/2X/3/3d9bdb78fe32452d1cbfd20f3e8a9464105fff2c.png)

Value : 200, getting 511, more then double of what I requested.

 ![200](https://europe1.discourse-cdn.com/victron/original/2X/3/3fc0d60e8756661083a2265f40b4d529bdd1df44.png)

Value : 500, getting 1168w, again more then double of what I requested.

 ![500](https://europe1.discourse-cdn.com/victron/original/2X/2/2f48a0ef1134b266ad4cbb5511023478c4b15aef.png)

I must be missing a big clue or have something misconfigured.

If it is normal behaviour can you please explain the logic behind it so I can take it into account when steering the charging/discharging of the battery.

Thanks!

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [1 January 2025 12:17 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/7 "2025-01-01T12:17:05Z")

</div>

> [@christophedm](#):
>
> misconfigured

Do you have a grid meter? Where is it physically vs where is it in software position?  
It is likely that as an issue.

Do you actually have loads on the output?

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [1 January 2025 14:53 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/8 "2025-01-01T14:53:37Z")

</div>

Maybe make a drawing how your system is connect to grid and house (grid meter?) ac loads, ac in, ac out 1/2?

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [1 January 2025 15:28 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/10 "2025-01-01T15:28:51Z")

</div>

Marc, here is the wiring.

 ![WhatsApp Image 2025-01-01 at 16.27.29](https://europe1.discourse-cdn.com/victron/original/2X/2/2c72e94aab64ad57f2b88b7b639634896d420863.jpeg)

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [1 January 2025 15:29 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/11 "2025-01-01T15:29:52Z")

</div>

> [@lxonline](#):
>
> Do you actually have loads on the output?

It is physically exporting that value, I can see it in the homewizard app, see my initial post, the one with the graphs purple and green.

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [1 January 2025 15:41 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/12 "2025-01-01T15:41:01Z")

</div>

You clearly dit not read the manual… get the ac out connection out asap, connect only ac in

why did you do that?😊

Thats causing weird issues

Whats connected to ve bus?

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [1 January 2025 16:00 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/13 "2025-01-01T16:00:46Z")

</div>

@DuivertNL I have removed the bridge between AC IN and AC OUT 1.  
Looks alot better now, I did read the manual but failed to find the info on which AC the feedback would occur, apparently it can just go out on the AC IN.

 ![image](https://europe1.discourse-cdn.com/victron/original/2X/c/cde2f0fb750978044b38cdfecd93510560a3cd6c.png)

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [1 January 2025 16:00 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/14 "2025-01-01T16:00:58Z")

</div>

> [@DuivertNL](#):
>
> Whats connected to ve bus?

MK3 to usb

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [1 January 2025 16:01 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/15 "2025-01-01T16:01:50Z")

</div>

You cant connect a mk3 at the same time with the GX running…

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [1 January 2025 16:02 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/16 "2025-01-01T16:02:32Z")

</div>

Yes its like a normal pv inverter so thats how it feeds back to grid

---

<div class="post-metadata">

**Author:** ![christophedm](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@christophedm](https://community.victronenergy.com/u/christophedm)\
**Post date:** [1 January 2025 16:05 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/17 "2025-01-01T16:05:42Z")

</div>

@DuivertNL the MK3 is just connected and wired through a cable gutter to an electric box, if I need it I can just grab it from there without needing to unscrew the Multiplus at the bottom again, I had already noticed it goes into “Blocked” when MK3 is connected.

Thanks for your help 🙂

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [1 January 2025 16:06 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/18 "2025-01-01T16:06:05Z")

</div>

Ok!

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [1 January 2025 16:43 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/19 "2025-01-01T16:43:48Z")

</div>

Also on the GX, you can switch in software ac output not in use as well. (Under ess settings)

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [15 January 2025 16:43 UTC](https://community.victronenergy.com/t/critical-loads-causing-excess-export-when-setting-modbus-register-37/17111/20 "2025-01-15T16:43:56Z")

</div>