Why it’s still on the manual if it’s not present anymore, I’m having issues with a EVCS and I’ve been struggling to find why it wasn’t available…

It’s still on the manual:

> **[5.2. VictronConnect setup, configuration and operation - 5. Setup,...](https://www.victronenergy.com/media/pg/EV_Charging_Station/en/setup,-configuration---operation.html#UUID-a5a30533-bc8a-55bb-2402-24b0532ac23f)**

---

<div class="post-metadata">

**Author:** ![Nicolas](https://avatars.discourse-cdn.com/v4/letter/n/67e7ee/32.png) [@Nicolas](https://community.victronenergy.com/u/Nicolas)\
**Post date:** [20 January 2026 17:48 UTC](https://community.victronenergy.com/t/cp-calibration-aborted/32978/22 "2026-01-20T17:48:58Z")

</div>

Hello @Juanito_G.  
Thank you for pointing this out, and sorry for the confusion it caused.  
The documentation will be updated in the near future to reflect the current behavior. Thank you for your patience and for bringing this to our attention.

---

<div class="post-metadata">

**Author:** ![jimboandthejetset](https://avatars.discourse-cdn.com/v4/letter/j/fbc32d/32.png) [@jimboandthejetset](https://community.victronenergy.com/u/jimboandthejetset)\
**Post date:** [11 April 2026 21:43 UTC](https://community.victronenergy.com/t/cp-calibration-aborted/32978/23 "2026-04-11T21:43:39Z")

</div>

I had the opposite problem - my EVCS was failing to switch its status to ‘Disconnected’ (on the web server and MQTT) when the cable was pulled out. Restarts, firmware downgrade, plugging and unplugging things didn’t resolve it. In the end I had to use Modbus to re-enable the facility to do a manual CP calibration which worked. I don’t understand why this has been disabled as default - a right PITA!

In case it helps anyone else, I did this in Home Assistant using the Modbus integration as it seemed the simplest solution and also enables me to monitor it and toggle it in the future if needed. The following yaml creates a sensor:

```auto
- name: victron_modbus_evcs
  type: tcp
  host: 192.168.xx.xx # IP address of EVCS 
  port: 502
  sensors:
  - name: 'CP Auto-Calibration State' # Writeable
    unique_id: cp_calib_state
    slave: 40 #HUB - Slave is device ID found when looking in the Device List on the Victron GX or VRM ID
    address: 5133 
    data_type: uint16 
    scan_interval: 20

```

An action (service call) can then be used to write the value, which can be done with automations/toggles if required:

```auto
     - action: modbus.write_register
       data:
         hub: victron_modbus_evcs
         address: 5133
         slave: 40
         value: 0

```

It’s a bit convoluted but works! I don’t know if firmware updates will revert the automatic status to to ‘1’ again, which hides the manual button?

---

<div class="post-metadata">

**Author:** ![alperen](https://avatars.discourse-cdn.com/v4/letter/a/e19b73/32.png) [@alperen](https://community.victronenergy.com/u/alperen)\
**Post date:** [18 August 2026 13:11 UTC](https://community.victronenergy.com/t/cp-calibration-aborted/32978/24 "2026-08-18T13:11:43Z")

</div>

**Subject:** EVCS-HQ2242XYGPY — Request to disable CP auto-calibration (Modbus register 5133) — recurring E-03 fault with specific EV

Hello,

We have an EV Charging Station, serial number **EVCS-HQ2242XYGPY** , firmware **v2.08 / 5.2**.

We are experiencing a recurring **E-03 (CP input short-circuit)** fault, but only when charging our **Togg T10F**. The fault appears specifically after charging current drops below 6A during PV Excess/Auto mode in cloudy conditions — charging stops and does not resume, and once the session ends the unit shows E-03 with the light ring red. Power-cycling the unit clears the fault temporarily, and it charges fine at a stable higher current, but the fault returns under the same low-current transition with this vehicle. Other symptoms and troubleshooting we’ve already tried are consistent with a CP tolerance mismatch specific to this vehicle’s onboard charger, rather than a wiring/installation fault.

We found this community thread describing a fix for a similar case: automatic CP calibration (introduced in firmware v2.02+) can be disabled by setting **Modbus register 5133 to 0** , which restores the manual “CP calibration” button so we can calibrate specifically with the T10F connected:

> [@CP Calibration - Aborted?](https://community.victronenergy.com/t/cp-calibration-aborted/32978):
>
> I have just installed an EVCS NS. First set up and firmware 2.0 complete, but I’m failing to get a connection between the EVCS and the vehicle (Mitsubishi Outlander PHEV). The type II cable is an Aptiv branded 32A single phase, and the resistances on the cable seem fine, though the PP line is possibly slightly high at 440ohm (measured with Fluke 324). When I try to Calibrate CP I have an error message returned : “Aborted! Calibration aborted by the user.” If I try to Calibrate CP with no cabl…

Could you please set register 5133 to 0 on our unit remotely, or advise the correct/safe procedure for us to do this ourselves? We’d like to run a manual CP calibration with the T10F connected under stable conditions.

Thank you,

---

<div class="post-metadata">

**Author:** ![Nicolas](https://avatars.discourse-cdn.com/v4/letter/n/67e7ee/32.png) [@Nicolas](https://community.victronenergy.com/u/Nicolas)\
**Post date:** [18 August 2026 18:23 UTC](https://community.victronenergy.com/t/cp-calibration-aborted/32978/25 "2026-08-18T18:23:29Z")

</div>

Hello @alperen. Yes, I can do that remotely, but I’m not sure it will help. It looks like another issue. Let’s try anyway, and let me also check your EVCS configuration. For that, you’ll need to invite me to your installation. I’ll send you a PM.