Hi All, I have a working system with 2xMP2, Pylontech battery and SmartSolar system.

Now during winter, I would like the system to ‘charge’ my batteries at a low charge current (max 2000W) from 30 up to 50%.

This way I prevent overload on the grid side, and keep my batteries healthy. I have enough with 50% SoC to make it to next morning.

Also, my minimum SoC is 20%, so then I fully connect to the grid. but then I need to avoid power peaking on ACout side, because if we use 15min more then 2500W from the grid, I have a higher power price to pay. with the help of my batteries I hope to avoid this.

Any ideas ? I am already starting to play with NodeRED, but I’m not able to figure out how to control the charger?

So, I also have ESS to inject y power to the grid. but when I activate the ‘charge schedul’e’ I’m not able to limit the charge power.

---

<div class="post-metadata">

**Author:** ![BjoernK](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/bjoernk/32/89_2.png) [@BjoernK](https://community.victronenergy.com/u/BjoernK)\
**Post date:** [27 September 2025 14:28 UTC](https://community.victronenergy.com/t/controlled-charging-system/46097/2 "2025-09-27T14:28:51Z")

</div>

Look for „power assist“ in docs and VEconfigure

---

<div class="post-metadata">

**Author:** ![bjorn.aenspeck](https://avatars.discourse-cdn.com/v4/letter/b/da6949/32.png) [@bjorn.aenspeck](https://community.victronenergy.com/u/bjorn.aenspeck)\
**Post date:** [27 September 2025 14:54 UTC](https://community.victronenergy.com/t/controlled-charging-system/46097/3 "2025-09-27T14:54:44Z")

</div>

Power assist is not the real item I need. I have considered thsi already.

I want to charge my battery from the grid, with a maximum 2400W power, from 30% up to maximum 50%

so, whenever my SoC reaches 30%, this ‘limited’ charger has to start working.

once reached 50% it should stop charging.

This to avoid my battery to drop to 20%, but still leaves me for using battery power when I use high power for short time.

What i mostly look for, is the NodeRed function to activate my MP2 devices to start charging my natteries but at limited power (2500W max)

---

<div class="post-metadata">

**Author:** ![kr0815](https://avatars.discourse-cdn.com/v4/letter/k/48db29/32.png) [@kr0815](https://community.victronenergy.com/u/kr0815)\
**Post date:** [27 September 2025 16:54 UTC](https://community.victronenergy.com/t/controlled-charging-system/46097/4 "2025-09-27T16:54:16Z")

</div>

you need 2 ations:

First, set max charge power to 2400W

Second, set desired SOC higher, so charging starts

Lok at the Node “Settings Control” - then select venus settings

Looks like you will have to give max Ampere instead of max Watt, but that should be easy to calculate

But i think your logic is wrong, power assist is the right way - otherwise maybe the dishwasher runs and you are over the 2500W limit

Also, if you set desired SOC to 30 % - it will never drop to 20% as long as there is AC Feed in available

---