Configuration problem with 3-phase MP2 system: suddenly incorrect settings, strange behaviour

Hello,

today I had to take a closer look at one of my 3-phase systems with MP2s, because it was behaving very strangely!

So first I downloaded the config via VRM, and noticed the following:

          mp2 1    mp2 2    mp2 3
ups       an       an       an
aes       aus      an       an
erdungsr. aus      an       an

I then disabled the UPS function and sent the change to all units (via VEConfigure and MK2), and checked via VRM. No change!

Next, I reconfigured the first MP2 using the MK2, saved the config, and then sent the same config to all 3 Multis. Everything seems fine for now. No idea where the problem came from, but rewriting the whole config usually helps in cases like this.

The reason for checking the config and reconfiguring was the system’s behaviour. Every now and then it would switch to inverter mode, then a few seconds later switch back to pass-through.

So I set up a graph with the key data and noticed that every time, before switching to inverter mode, the battery was being charged, even though I’d set the charger to off on all units in the last config change. On top of that, the charge voltage was set to 49 V, so the battery would only be charged if the SOC was too low, and the charge current was set to 2 A. Even so, 1–2 A was still being sent to the battery at 52 V, and the system switched over!

But even with an SOC of 100% and the maximum charge voltage, switching over—presumably to interrupt or stop charging—wouldn’t have been necessary, since there are three inverter systems and DC/DC converters connected to the battery. A charge current of 1–2 A wouldn’t have raised the charge voltage anyway, and the MPPTs would have supplied correspondingly less current, since they’re voltage-controlled!

So why did the system switch from pass-through to inverter mode?

I’ve already found that you can force an MP2 to charge even in inverter-only mode by feeding power into AC-out. But here, only the house is connected to AC-out, with no other inverter that could feed power in. And in pass-through mode, the unit should follow the voltage at AC-in, not try to influence it.

I also disabled PowerAssist while I was at it, as I’ve had problems with that before too. For now, I’ll let it run idle and later disable the bypass again, hoping the reconfiguration has fixed the problem. If not, I’ll probably install a firmware update. This is the system with the oldest firmware anyway: 470.

Has anyone had similar problems before?

Bye

The “Send to all devices” function doesn’t work in certain configurations, so in my opinion you should always send to each device individually.

Hi,

The second time, I changed the downloaded config for each device individually and uploaded it again, but the result was the same.

So I adjusted the config from the first device, which was correct, and then uploaded it to each MP2 individually via veconfig. The values have been correct ever since.

The only question is why the values were suddenly wrong. I’ve read them via the VRM quite a few times to check or change settings, but I’ve never had the second and third Multi suddenly end up with a few completely wrong and non-working settings before!

Bye

Good evening,

First a question, do you want the earth relays on or off, pending your setup.

Either setting will not create an issue between the inverters, even if just one is switched on, and/or any combination.

Then the UPS on or off, all should be on or all off, pending your choice.

The AES function should be off in 3 phase, as that only works in mono phase, and might do strange things, so, that’s definitely to set to off.

As, above, Victron advices NOT to update 3 phase installs through VRM, only locally and individually one by one…as we always do…its in the manuals for updates written…

First take out the parameters one by one, then update new firmware one by one, then put the parameters back one by one, easy, 20 minutes work.

But, yes, when you have 30 inverters (3 phase X 10 par), it takes about half a day, not your case…

Regards, Jeroen.

Hi,

the grounding relay would cause problems, because it would put the system into a state that isn’t permitted, as the input and output Ns are bridged! That’s why I’ve disabled it on all the Multis!

There’s only one system where it will be enabled later, once it’s configured as an ESS. It’s normally not a problem if N and PE are connected at multiple points, especially if this is upstream of the first loads, but it still isn’t permitted!

Unfortunately, the UPS function causes problems for me, as I have several systems connected in series, and when the load changes significantly, the UPS function gets activated. And you can probably imagine what would happen in the worst-case scenario if a system with 3 x MP2 5000 units switched to inverter mode because the UPS function was triggered, with a load of over 6 kW per phase!

It wouldn’t matter whether AES was on or off, since the base load is higher than what’s needed for AES. Besides, there’s voltage on AC-in, so AES wouldn’t work anyway!

I’ve updated three-phase systems via VRM several times, and it works without any problems. And don’t forget, the update doesn’t actually run through VRM; it runs through the GX, which just receives the command to do it. Besides, if you weren’t supposed to use this, Victron probably wouldn’t have built it into VRM!

With my old MP 5000s, it also took some time, since I had the PC connected in the office, while the inverters were installed in the garage. So I had to do a lot of walking back and forth!

But that has nothing to do with the problem that occurred: the device’s configuration changed by itself, and I could only correct those changes by completely overwriting the configuration!

Bye

Could it be that, in a 3P system, certain states in the slaves take on default values because they’re controlled by the master anyway?

So I wrote the master config to the slaves, and in the ESS-Assi the byte size is smaller in the slaves. Ergo, a 3P slave doesn’t take over everything.

Hi,

the ESS is always controlled by the master, so certain settings are only configured on the master!

However, this doesn’t apply to other configuration settings, apart from certain assistants.

Bye

Good evening,

Straight out of your Victron inverter manual;

AES (Automatic Economy Switch).

If this setting is turned “on”, the power consumption in no-load operation and with low loads is decreased by approx. 20 %, by slightly “narrowing” the sinusoidal voltage. Not adjustable with DIP switches. Applicable in stand-alone configuration only.

Better to just switch it off in 3 phase.

Regards, Jeroen.

Hello,

I haven’t enabled it anywhere either, but suddenly it was switched on for two phases. No idea why.

It wouldn’t work for me anyway, because the base load is too high for it, and if it weren’t, the connected devices wouldn’t work properly in the second energy-saving mode.

Goodbye

Hello,

AES saves power in off-grid mode at low loads by modifying the sine wave.
When the system is grid-connected, the grid sets the frequency and the system MUST “fall into line”. In other words, the AES setting has no effect whatsoever in grid-connected mode, whether it is on or off, whether it uses a modified sine wave or search mode…

Hello,

I know. But I always have several inverters connected in series, so I can’t use AES for that reason alone!

And then there’s also the fact that the minimum energy requirement per phase averages over 100 W.

Bye