Hello,
today I had to take a closer look at one of my 3-phase systems with MP2s, because it was behaving very strangely!
So first I downloaded the config via VRM, and noticed the following:
mp2 1 mp2 2 mp2 3
ups an an an
aes aus an an
erdungsr. aus an an
I then disabled the UPS function and sent the change to all units (via VEConfigure and MK2), and checked via VRM. No change!
Next, I reconfigured the first MP2 using the MK2, saved the config, and then sent the same config to all 3 Multis. Everything seems fine for now. No idea where the problem came from, but rewriting the whole config usually helps in cases like this.
The reason for checking the config and reconfiguring was the system’s behaviour. Every now and then it would switch to inverter mode, then a few seconds later switch back to pass-through.
So I set up a graph with the key data and noticed that every time, before switching to inverter mode, the battery was being charged, even though I’d set the charger to off on all units in the last config change. On top of that, the charge voltage was set to 49 V, so the battery would only be charged if the SOC was too low, and the charge current was set to 2 A. Even so, 1–2 A was still being sent to the battery at 52 V, and the system switched over!
But even with an SOC of 100% and the maximum charge voltage, switching over—presumably to interrupt or stop charging—wouldn’t have been necessary, since there are three inverter systems and DC/DC converters connected to the battery. A charge current of 1–2 A wouldn’t have raised the charge voltage anyway, and the MPPTs would have supplied correspondingly less current, since they’re voltage-controlled!
So why did the system switch from pass-through to inverter mode?
I’ve already found that you can force an MP2 to charge even in inverter-only mode by feeding power into AC-out. But here, only the house is connected to AC-out, with no other inverter that could feed power in. And in pass-through mode, the unit should follow the voltage at AC-in, not try to influence it.
I also disabled PowerAssist while I was at it, as I’ve had problems with that before too. For now, I’ll let it run idle and later disable the bypass again, hoping the reconfiguration has fixed the problem. If not, I’ll probably install a firmware update. This is the system with the oldest firmware anyway: 470.
Has anyone had similar problems before?
Bye