PV array: 2 strings of 5× Jinko 425 W (Isc ≈ 13.5 A per string)
Each string: 20 A two-pole gPV fuse → connected in parallel → Noark 50 A DC isolator → 1 MPPT only
Generator Iscmax = 33.8 A (1.25 × 13.5 × 2)
Feedback from Consuel (Table 1, row A of the SC-144C-5):
“the 20 A rating of the main PV cable is unsuitable for the Iscmax current of 33.8 A”
Here’s what I think I understand: the 20 A is my protection per string (≈ 13.5 A/string), whereas 33.8 A is the current from the generator (the 2 combined strings) flowing through the main cable downstream of the fuses.
My questions:
For 2 strings + battery + one Victron MPPT (which blocks reverse current), are my two 20 A string fuses sufficient, or do I also need protection on the main cable, rated for the Iscmax?
If main cable protection is required: a ~40 A gPV fuse or a DC circuit breaker? Does a circuit breaker make sense given that the PV current is self-limiting?
How have you resolved this type of refusal with Consuel: by adding equipment, or simply by rewording the form/diagram?
I entered 33.8A. Actually, the help says the maximum current of a PV string is 13.5A for me, but it also says 33.8A for the PV generator, so the help isn’t very clear. Is this purely informational, in which case I should enter 13.5A, or do I have a protection issue and need to replace the Noark 50A isolator?
Stef_POLLAK
(sites-autonomes.fr & Team Victron Formation)
4
Could I have a copy of your completed SC-144C-5 file?
That’s one of the things that was better in the old folder! Here you have to enter the chain! In the old folder, there were two lines, one for the chain and one for the generator!
So, what should I do about my protection setup? I’ll edit my post, because I didn’t understand your answer, Thierry—am I just supposed to specify 13.8 A or something else? Ha, just so you know, I’m connecting my two strings in parallel to the EasySolar 2 GX.
I’m getting back in touch because I received Consuel approval on 31 August 2026. What really surprised me was the inspection, which lasted 10 minutes, watch in hand.
The inspector explained that he covers all of department 77 as well as part of department 93.
He didn’t seem particularly well trained in IT earthing systems, and didn’t seem willing to carry out the necessary physical checks. He simply asked me to tell him where the various components were, such as the CPI, the PV protection devices and the house’s earth connection. Oh yes, he did take out a huge portable machine to check something or other on the inverter casing!
He asked me to add a label to the trunking through which the cables from the panels run to the DC enclosure! And he checked the labels…