# Cerbo random reboots - multiple times daily

**URL:** <https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833>\
**Category:** DIY\
**Tags:** expert, gx\_device, marine, cerbo\_gx\
**Created:** [24 February 2026 11:37 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833 "2026-02-24T11:37:18Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![NFBR](https://avatars.discourse-cdn.com/v4/letter/n/e19b73/32.png) [@NFBR](https://community.victronenergy.com/u/NFBR)\
**Post date:** [24 February 2026 11:37 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/1 "2026-02-24T11:37:19Z")

</div>

My Cerbo reboots randomly multiple times daily when Large Image is installed

Tests done

- Standard Image - no reboot
- 3 different Cerbo units, v1 and v2 - random reboots
- 48V vs 12V supply - random reboots
- Extra fan cooling - random reboots
- Factory reset - random reboots
- USB Hub changed 3 times - random reboots
- MicroSD - removed / changed - random reboots

Large Image - no config / modules - default image

50 Display  
1 x VE.Bus Inverter  
1 x MK3 USB Inverter (USB)  
1 x VE.Direct Inverter (USB)  
2 x BMV712 ve.direct  
1 x Smartshunt ve.direct  
GPS (USB)  
Bluetooth (USB) for 2 x Ruuvi Sensor  
7 x MPPT ve.direct (USB)  
VE.CAN to WS500 & Zeus  
Wired Ethernet  
USB Hub is powered.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 February 2026 11:39 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/2 "2026-02-24T11:39:14Z")

</div>

Many topics on this subject worth a look.  
Check you don’t have reboot on comms loss enabled in settings.  
After that you will need to dig around in logs to find out more, most of this is discussed in existing topics already.

You have a lot of devices and multiple inverters, that won’t be helping and might be pushing the system resources.

---

<div class="post-metadata">

**Author:** ![fredvduin](https://avatars.discourse-cdn.com/v4/letter/f/ed655f/32.png) [@fredvduin](https://community.victronenergy.com/u/fredvduin)\
**Post date:** [24 February 2026 12:47 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/3 "2026-02-24T12:47:32Z")

</div>

> [@NFBR](#):
>
> when Large Image is installed

And with the small image you have no random reboots?

---

<div class="post-metadata">

**Author:** ![NFBR](https://avatars.discourse-cdn.com/v4/letter/n/e19b73/32.png) [@NFBR](https://community.victronenergy.com/u/NFBR)\
**Post date:** [24 February 2026 13:05 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/4 "2026-02-24T13:05:10Z")

</div>

Correct

---

<div class="post-metadata">

**Author:** ![NFBR](https://avatars.discourse-cdn.com/v4/letter/n/e19b73/32.png) [@NFBR](https://community.victronenergy.com/u/NFBR)\
**Post date:** [24 February 2026 13:06 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/5 "2026-02-24T13:06:11Z")

</div>

VRM loss reboot is not enabled  
I can’t find anything in logs, but maybe haven’t dug deep enough  
I have been through all the threads - none seem to align.  
It didn’t used to, so it’s within the last 6mths that it’s started - leading me to think it’s OS version related

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 February 2026 13:07 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/6 "2026-02-24T13:07:36Z")

</div>

There is an OS log you can get to via ssh.  
If it is a watchdog restarting it, it will be in there.  
But if its stable on the small image then it is resource related, since you haven’t configured anything like nodered or signalk to start.  
Versions get heavier as they get newer, so pretty easy to cross a threshold that you were just beneath previously.

There is a custom widget on VRM advanced for the GX - dbus roundtrip time. If it is high there is a resource issue. It will be stored historically on vrm.

---

<div class="post-metadata">

**Author:** ![kr0815](https://avatars.discourse-cdn.com/v4/letter/k/48db29/32.png) [@kr0815](https://community.victronenergy.com/u/kr0815)\
**Post date:** [24 February 2026 13:11 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/7 "2026-02-24T13:11:25Z")

</div>

i had the same problem, tried many things

i found this thread:

> [@Unwanted Reboots](https://community.victronenergy.com/t/unwanted-reboots/40839/10):
>
> I found, that the gui-v1 service is occasionally consuming quite some cpu, despite i’m no longer using it. svc -d /service/start-gui stops it, but be aware that this also terminates the vnc service, used to display the remote-console (for either version) through vrm. Then, you can only access the local ui remotely when you have a vpn connection and can access the device ip directly. Other than that, do a df -h and check the remaining disk space on the root partition. With the large image, th…

i set watchdog triggers higher - since then - problem gone

Dou have the GUI locally open on your PC?

This consumes a lot of Resources (even if it´s just an open Tab in the Browser background)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [24 February 2026 13:15 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/8 "2026-02-24T13:15:15Z")

</div>

Also worth disabling this:

 ![Screenshot 2026-02-24 at 15.14.17](https://europe1.discourse-cdn.com/victron/original/3X/4/5/45cab36612bf9e83084bdd92fa4afb6cdc76679b.png)

---

<div class="post-metadata">

**Author:** ![NFBR](https://avatars.discourse-cdn.com/v4/letter/n/e19b73/32.png) [@NFBR](https://community.victronenergy.com/u/NFBR)\
**Post date:** [24 February 2026 13:29 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/9 "2026-02-24T13:29:36Z")

</div>

Only the local screen

---

<div class="post-metadata">

**Author:** ![fredvduin](https://avatars.discourse-cdn.com/v4/letter/f/ed655f/32.png) [@fredvduin](https://community.victronenergy.com/u/fredvduin)\
**Post date:** [24 February 2026 16:48 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/10 "2026-02-24T16:48:38Z")

</div>

The large image uses more resources.

Have you enable Node Red and ““Access MQTT””?

If you do not used them disable the services

There is a watchdog timer when you use high resources =\>system reboots.

How to check watchdog reboots.

Login ssh

cd /data/log

grep “shutting down” \*

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/7/078e8cc7f02ad80088a80ac4969839096846c4da.png)

(I have problems …….too……)

error- daemon.err watchdog[469]: loadavg 8 7 4 is higher than the given threshold 0 6 6!

![image](https://europe1.discourse-cdn.com/victron/original/3X/3/5/354e901968695e971c0f1976cf54136b25eb430b.png)

How check average

command uptime

![image](https://europe1.discourse-cdn.com/victron/original/3X/5/8/584f5472cdb5afa8c842657245aa029c1e889aac.png)

For trouble shouting there is a process file (last reboot)

/data/log/watchdog\_processlist.txt

More info how to change config (is not the solution…)

> **[Cerbo GX still rebooting multiple times a day even after the firmware update...](https://communityarchive.victronenergy.com/questions/308702/cerbo-gx-still-rebooting-multiple-times-a-day-even.html)**

Example

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/d/0/d05ac00cf71b5f3645f70725d878e12de8f4249b.png)

---

<div class="post-metadata">

**Author:** ![kr0815](https://avatars.discourse-cdn.com/v4/letter/k/48db29/32.png) [@kr0815](https://community.victronenergy.com/u/kr0815)\
**Post date:** [24 February 2026 17:15 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/11 "2026-02-24T17:15:00Z")

</div>

this is my uptime log

I changed the watchdog config end of last month

(config has to be changed after each update)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/b/1/b1412e02df8f081eaea9c9932e2ef987c4da24dd.png)

---

<div class="post-metadata">

**Author:** ![NFBR](https://avatars.discourse-cdn.com/v4/letter/n/e19b73/32.png) [@NFBR](https://community.victronenergy.com/u/NFBR)\
**Post date:** [17 March 2026 15:25 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/12 "2026-03-17T15:25:02Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/0/9/091c8150f870a2893391588b03838c5867961f8d.jpeg)Tracked it CPU and watchdog - disabled animations solved it.

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [31 March 2026 15:25 UTC](https://community.victronenergy.com/t/cerbo-random-reboots-multiple-times-daily/53833/13 "2026-03-31T15:25:48Z")

</div>

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.