Cegasa E/Bick Batteries - RS 450/200 Solar Charger Causing Battery Fault

New installation with bank of three E/Bick batteries (48V, 3x13KWH) and RS 450/200 Solar Charger:

Initial startup went fine with the bank at ~95% SOC. The battery has a pre-charge function that brings the buss up to ~48V before closing the internal contactors.

After running normally for a couple days, the bank was at 100% SOC and the system was shut down for some wiring work.

The bank then failed to re-start. The bank would fault out during pre-charge and trip out. Pulling the battery fuse for the RS would allow the battery to startup. I initially thought the RS had an internal fault, but that was not the case. With the battery bank offline, the RS would power the buss to ~48V just fine.

Testing showed the buss voltage would climb during pre-charge as expected, but as soon as there was enough voltage (~10V) the Cerbo & display would start to power up. The RS would then show up on the display. A few moments later, the “external control” tag would appear on the RS. Simultaneously, the bus voltage would ramp down and the battery faulted out, failing to complete pre-charge.

Similarly, if the RS was powered up first, the buss was ~48V from solar power. As soon as the battery was started, the RS would switch to external control and the buss voltage would taper down to ~30V. The battery would then trip out during pre-charge.

I then unplugged the CAN from the RS and tried again. This time the buss voltage climbed steadily during pre charge to ~48V and the battery came online normally. I plugged the CAN back in, the RS switched to “external control” and everything was fine.

My theory is that, being at 100% SOC, as soon as the RS switched to external control it was somehow trying to hold/lower the buss voltage down to prevent charging, fighting the pre-charge.

Perhaps a delay needs to be implemented it the switch to external control?

Thoughts?