Cebro update to v3.72 ? trouble?

Hello,

Yesterday I performed the Cebro update from v3.71 to v3.72. Everything went smoothly; however, now that the sun is shining, the power is going to the grid instead of to the BATTERY. The Energy Storage System (ESS) is enabled and in green mode, the battery status is 19%, and the Cebro charge target is also 19% (normally, I believe, it is at 0%). What is wrong with version v3.72? Now I would like to revert to version v3.71. How?

3-phase MPII 6K5 battery Seplos 560

On the Cerbo go to

Settings/ General / Firmware / Stored backup firmware

and you should see V3.71 listed with a “press to boot” button next to it.

Unfortunately, for me that option consists of 2 x V3.72

Is there another option? The Victron Professional site only lists version v3.72; please provide your input.

You could try V3.80~9 beta.

Download the required version from Victron Professional and install them with a USB stick or SD card.

The list at Victron Professional, no v3.80 beta or v3.71, only 3.72, but I want to get rid of that.

any other suggestions

perhaps reading “Archive of older Venus OS versions.txt”?

Thank you very much for your suggestions. I have found the file and am going to install it. Thanks again.