ABB CM-IWN.5 wiring

Hello everyone.

I currently have an MPPT 250/70 TR connected to 6 PV panels in 3S2P, east/west-facing.

For the safety of equipment and people, I bought an “IMD” ABB CM-IWN.5S ..1SVR750660R0400.

For the wiring, I plan to proceed as follows:

Power supply = A1: connected to the positive 48 Vdc battery terminal via a 2 A gG fuse; terminal A2: connected to the negative battery terminal (busbar)

PV measurement = with 2.5 mm² flexible wire on L+ and L-, connected downstream of the 25 A circuit breaker for the 6 PV panels.

Earth connection = the IMD’s earth terminal directly to the earth terminal block (connected to the house earth), and terminal KE connected to that same earth terminal block, where all the AC/DC earths are connected.

To disconnect the MPPT 250/70 TR, I’ll connect to terminals H and L of the “remote”, using 1.5 mm² wire from terminals 11 and 14 of the ABB. The ABB DIP switches will be set as follows: DIP 1 = on, DIP 2 = on, DIP 3 = on and DIP 4 = off.

The ABB resistance adjustment dials would be set to R1.1 = 20 kΩ and R1.2 = 10 kΩ.

The end goal is that, if there’s a problem on the PV line, the ABB disconnects the MPPT 250/70, and a human intervention is required to restart it after the PV array has been repaired/checked.
Can anyone tell me whether this wiring and setup comply with the requirements of the standard (Consuel), given that this PV array is subject to the rule that an IMD is mandatory at >= 120 Vdc?

Hello @yvon62,

Have you checked that the voltage of the module string to be monitored is below 600 V?
Including taking into account the increase in voltage at sub-zero temperatures (a factor of 1.2 or the UTE formula).

Can you tell us how much you found this product for? It could be an alternative to the DOLD IL 5881, but with a higher DC input voltage (600 Vdc compared with just 280 Vdc for the IL 5881).

Hello Stef_POLLAK, thanks for your interest.

Yes, I checked, and I’m going for 3 PV panels in series, MAX =190Vdc.44. The ABB takes up to 600Vdc according to the manual.

I found one for 90 euros (second-hand) .. but I’m stuck on the wiring: “should I fit a double-pole fuse protection on L+ and L- (to protect the flexible 2.5mm² wires) — and, above all, what type of fuses: gG, gPV or something else?”

Right, I’ve decided to fit a 2-pole fuse holder with two 2 A gPV fuses just before the input, downstream of the 25 A PV circuit breaker, for the flexible 2.5 mm² L+ and L− wires… I hope I’m not making a mistake!!

I would have suggested using a larger cable cross-section, but apparently the device won’t accept anything larger than 2.5 mm².

Looking at the datasheet, the diagram shows that you don’t need to add another protective device if your module string is already protected upstream…

Hello, and thanks for your reply Stef_POLLAK,

If I read the manual correctly, you can use up to 4 mm²? Solid conductor?

But regarding the protection of L+ and L-, if the wires touch because of a rodent, overheating, etc., isn’t protection for the wires themselves necessary/mandatory?

On that side of the installation, flexible cable is normally used.

If your string is already protected by gPV fuses, your equipment is protected, since the energy at that point comes from the modules.

Hello and thank you Stef_POLLAK for your reply. I’d like to make sure I’ve understood correctly: do the gPV string fuses also protect the CPI’s L+ and L− measurement wires when they are connected downstream of the common 25 A PV circuit breaker? The MPPT-to-protection-to-PV path and distances are: MPPT 250/70 → 1 metre → Schneider DC 25 A breaker → 15 m → PV DC enclosure = 2-pole gPV fuses.

With two strings in parallel, is this protection still sufficient in the event of a short circuit on one of the measurement wires, or is specific protection needed for this branch?

I mainly want to know whether connecting directly to the L+/L− inputs of the ABB CM-IWN.5S complies with the manufacturer’s specifications, without adding unnecessary fuses.

I can see in this discussion ( Question CPI "arret d'urgence" sur Victron et norme d'utilisation - #10 by Etienne ) that Mr Thierry Cortassa mentions a maximum voltage of 24 V DC for the relays on the ABB CPI… so I’m a bit confused… Does this mean that, with my wiring configuration, I can’t connect the ABB CPI? What voltage or current is applied to the Remote L/H terminals on the 250/70-Tr model? Can I connect terminals 11 and 14 on the CPI to terminals H and L on the remote input of the MPPT 250/70 TR?