Battery Isolation/Cutoff Switches and Fusing

Greetings! I’m looking for some help/guidance on my planned system:

4 x 300ah 12.8v lifepo4 batteries, connected parallel, then parallel to:

1 x Lynx Class T Power in (4/0 wire), then

Lynx Shunt, then

Lynx Distributor, connected to:

Victron Multiplex 12v 4000va 160-50 2x120

Question: re Isolation/Cutoff switches for batteries…should I bother to try to put them in? (cable run from batteries to Power in is maybe 3 ft.), or just utilize the class T fuses to isolate the batteries?

Also, is the correct method to use MRBF fuses on each battery prior to the connection to the Power in?

Thanks a ton…DDoig

I decided to fuse every battery individually with a good fuse.
Having multiple unfused batteries in parallel would present a problem if any one of them went short or low voltage.

It is very handy to be able to disconnect the batteries before they go into the rest of the system when servicing it. Removing the fuse gives the same results but is a lot less convenient. I would highly recommend installing a shut off.
As far as using an MRBF on each batteries positive terminal, yes, that is technically correct.