# Batteries not charging to 100% overnight

**URL:** <https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746>\
**Category:** Q&A and troubleshooting\
**Tags:** bslbatt, beginner\
**Created:** [27 October 2025 14:11 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746 "2025-10-27T14:11:49Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![tomwatkins2025](https://avatars.discourse-cdn.com/v4/letter/t/c37758/32.png) [@tomwatkins2025](https://community.victronenergy.com/u/tomwatkins2025)\
**Post date:** [27 October 2025 14:11 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746/1 "2025-10-27T14:11:49Z")

</div>

Hello Victron Community

We’ve completed 3 installations so far (panels and batteries) at locations in the south west of England.

Our recent installation is set up to charge batteries overnight (2:00-5:00). Is there any reasons why the batteries should not be getting to 100%, at the moment they only charge to about 70%?

Many Thanks

---

<div class="post-metadata">

**Author:** ![dansz](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/dansz/32/12006_2.png) [@dansz](https://community.victronenergy.com/u/dansz)\
**Post date:** [27 October 2025 14:36 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746/2 "2025-10-27T14:36:26Z")

</div>

Could you post the CCL and DCL values from advanced dashboard?

---

<div class="post-metadata">

**Author:** ![tomwatkins2025](https://avatars.discourse-cdn.com/v4/letter/t/c37758/32.png) [@tomwatkins2025](https://community.victronenergy.com/u/tomwatkins2025)\
**Post date:** [27 October 2025 15:17 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746/3 "2025-10-27T15:17:55Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/c/c/ccc752cfe45ce9db4af26a162bc1405e3f79a620.png)

---

<div class="post-metadata">

**Author:** ![tomwatkins2025](https://avatars.discourse-cdn.com/v4/letter/t/c37758/32.png) [@tomwatkins2025](https://community.victronenergy.com/u/tomwatkins2025)\
**Post date:** [27 October 2025 15:18 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746/4 "2025-10-27T15:18:50Z")

</div>

Hello dansz

Is this helpful?

and thanks 👍

---

<div class="post-metadata">

**Author:** ![dmajwool](https://avatars.discourse-cdn.com/v4/letter/d/7ba0ec/32.png) [@dmajwool](https://community.victronenergy.com/u/dmajwool)\
**Post date:** [28 October 2025 17:50 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746/5 "2025-10-28T17:50:07Z")

</div>

Hi Tom, Silly question:  
Have you ruled out the possibility that the charger simply runs out of time at 05.00?

---

<div class="post-metadata">

**Author:** ![DuivertNL](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/duivertnl/32/279_2.png) [@DuivertNL](https://community.victronenergy.com/u/DuivertNL)\
**Post date:** [28 October 2025 18:03 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-overnight/47746/6 "2025-10-28T18:03:06Z")

</div>

I think thats the case here too

3 hours is a short time