**Configuration**

- MultiPlus-II GX 48/5000/70-50 Firmware 2623556
- Pylontech Batteries 28.5Kw/h (7 batteries 3 x us5000C, 3 x us3000C)
- Solax PV Inverter (Energy meter via RS485)
- VM-3P75CT (Energy meter)
- 1 x ESS Charging Schedule (23:30 =\> 05:30 100% charge)

**Problem Statement**

The system has been working as expected with the ESS schedule charging the batteries to 100% between **23:30** and **05:30**. As of the 19th November the system only charges the batteries to around 75%. Charging starts of correctly at around 11% / per but tails off to **5%** and **2%** as it gets closer to the 75% mark. At no point over the last week has the system charged to above 77%.

The system configuration **has not been changed** in months so I am at a complete loss as to why this is happening.

The following is from my excel spreadsheet showing the delta charge rate from the last week

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/b/c/bccf087a17c44dc5a0e8816995ac057c9b5d1a02.png)

Todays charging showing the tailing off as 75% is reached

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/5/b/5bde959b0c1ee9651d7fa9987fe010725eb544ea.png)

Charging prior to 19th November (No tailing off of charge rate)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/1/2/12c1457fcc4a0219529040f152c5eec6b0074abb.png)

Help would be appreciated .

Steve W

---

<div class="post-metadata">

**Author:** ![mac](https://avatars.discourse-cdn.com/v4/letter/m/cc9497/32.png) [@mac](https://community.victronenergy.com/u/mac)\
**Post date:** [25 November 2025 13:41 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-no-change-of-configuration/49270/2 "2025-11-25T13:41:51Z")

</div>

> [@wrightste](#):
>
> At no point over the last week has the system charged to above 77%.

What is the SOC of the individual batteries?

---

<div class="post-metadata">

**Author:** ![wrightste](https://avatars.discourse-cdn.com/v4/letter/w/858c86/32.png) [@wrightste](https://community.victronenergy.com/u/wrightste)\
**Post date:** [25 November 2025 14:05 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-no-change-of-configuration/49270/3 "2025-11-25T14:05:12Z")

</div>

Is there an easier way to monitor the individual batteries using the **SERVTEC 3.5m USB Diagnostic cable** and associated software?

---

<div class="post-metadata">

**Author:** ![wrightste](https://avatars.discourse-cdn.com/v4/letter/w/858c86/32.png) [@wrightste](https://community.victronenergy.com/u/wrightste)\
**Post date:** [25 November 2025 16:03 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-no-change-of-configuration/49270/4 "2025-11-25T16:03:08Z")

</div>

![image](https://europe1.discourse-cdn.com/victron/original/3X/a/3/a3b140a8f3a22c00beb1544d4676f792495bc4af.png)

P1 55%  
P2 62%  
P3 52%  
P4 41%  
P5 71%  
P6 48%  
P7 60%

So yes the batteries appear to be all over the place

---

<div class="post-metadata">

**Author:** ![mac](https://avatars.discourse-cdn.com/v4/letter/m/cc9497/32.png) [@mac](https://community.victronenergy.com/u/mac)\
**Post date:** [25 November 2025 16:23 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-no-change-of-configuration/49270/5 "2025-11-25T16:23:10Z")

</div>

Looks like one or a couple of batteries are limiting charging, could you try to keep charging until they are all 100% ?

Also low temperature can limit charge current.

---

<div class="post-metadata">

**Author:** ![wrightste](https://avatars.discourse-cdn.com/v4/letter/w/858c86/32.png) [@wrightste](https://community.victronenergy.com/u/wrightste)\
**Post date:** [25 November 2025 17:06 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-no-change-of-configuration/49270/6 "2025-11-25T17:06:43Z")

</div>

I’m out tomrrow so I’ll give it a go on Thursday. The coldest the batteries have been is 5C as they are in an insulated rack with a heater that cuts in at 5C. The betteries used to be in a plant room in the house but ran out of space to add the two extra US5000Cs. The batteries are in a 72U 19” rack which is insulated and there is a heater. The thermostat may be a bit low at 5C so I will increase it to 10C.

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/2/02048a2b93343eaf3b429098daa1e631beac9a1b.png)

---

<div class="post-metadata">

**Author:** ![wrightste](https://avatars.discourse-cdn.com/v4/letter/w/858c86/32.png) [@wrightste](https://community.victronenergy.com/u/wrightste)\
**Post date:** [28 November 2025 08:09 UTC](https://community.victronenergy.com/t/batteries-not-charging-to-100-no-change-of-configuration/49270/7 "2025-11-28T08:09:44Z")

</div>

It was my intention, yesterday, to float the batteries to the same level, however the battery behavious has returned to normal and there is no tail off and the batteries charge to 100%. I have checked the SOC of the batteries and the original imblanace is still present.

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/8/c/8c44976f36de0ea4b56db3cd5915cd8d4f59be90.png)

 ![image](https://europe1.discourse-cdn.com/victron/original/3X/0/9/0934798da7ad06947a40c5653a596b96a9a2a382.png)

The weather has got warmer and I have increased the temperature in the cabinet to 10C. I am also changing the heater to one that has a larger capacity and a fan to provide even heating,