Batteries discharge too low even after cutoff voltage (own MP consumption)
Hello folks !
We use Multiplus 1600VA/48V and 3000VA/48V as UPS backup for our toll applications on highway.
I set cutoff voltage to approx 43V, so when cutoff is reached ACOUT is disconnected and invertor disabled. Even that, there is still power consumption around 25mA and it happened that this consumption drained batteries so low they are damaged now. It is not regular situation, but it can happen and i want some mechanism to prevent this.
I also tested the remote contact on multiplus, when disconnected, consumption is only 2mA which is much better, but i dont know how the mechanism should be designed to be automated. There are lot of sites and is not easy to go there (cost money, time).
I would like ask you what you reccomend to prevent battery drain after cutoff (without AC-in for longer time) but it should still be automated so when AC-in appear batteries will be connected and Multiplus will start charging them. Is there official Victron solution ? is possible to do it via Multiplus Assistants ?
Thank you in advance
Filip
Check whether PV can be added at these sites.
At least with the DC-coupled PV, it’s possible to black-start the system.
What’s currently configured? Intentional islanding?
There’s a GX device as well, right? The system probably isn’t measuring the low standby current correctly. That’s why the calculation doesn’t work.
Hi Karl
Thanks for the reply! To clarify a few points:
  1. PV addition: Adding PV panels is unfortunately not an option for these highway toll sites due to space/location constraints and fixed installation requirements.
  2. Current measurement: The 25mA idle drain in low-voltage cutoff state was measured directly with a calibrated multimeter, not read from software or GX calculations. When the MultiPlus triggers low-voltage cutoff, the internal logic and monitoring stay active, drawing around 25mA @ 48V (~1.2W continuously), which will slowly deep-discharge the battery over extended power outages.
  3. Remote contact: When opening the Remote On/Off contact, consumption drops down to 2mA (the sleep state).
My main goal is to find an automated way to disconnect or switch the MultiPlus into this low-power / turned-off state once DC cut-off is reached, AND have it automatically wake up / start charging once AC-in power returns.
Is there a recommended Victron relay setup or Assistant configuration (e.g. driving an auxiliary relay or programmable relay tied to the Remote terminal) that can achieve this automatic recovery upon AC-in detection? I have some idea to put external relays on ACIN and ACOUT and drive the relay which will disconnect/connect battery. But firstly i wanted check if there is already some solution.
40 days is about 1,000 hours. So 25 Ah would be used during that time. Is the battery too small or not charged properly? Perhaps very poorly balanced?
To clarify: the 25mA drain does not start with a fully charged 83Ah battery.
The 25mA continuous drain occurs AFTER the MultiPlus reaches the 43V cutoff and disables the AC output. At 43V (approx. 2.68V per cell for a 16S LiFePO4 pack under load), the battery is already at 98–99% DoD (Depth of Discharge).
At that point, there are only about 1 to 2 Ah of remaining capacity left in the cells.
  • At 25mA drain: 2 Ah / 0.025A = ~80 hours (around 3 days) until the battery is drained to absolute 0V and permanently destroyed.
  • At 2mA drain (Remote OFF): 2 Ah / 0.002A = ~1000 hours (over 40 days), which gives service teams enough time to react and restore power before cell damage occurs.
So the issue isn’t battery sizing or poor balancing during normal operation. The problem is that after a legitimate power grid blackout drains the battery to 43V, the MultiPlus stays in a standby/fault state drawing 25mA, which completely kills the remaining 1–2 Ah within a couple of days if AC grid power isn’t restored in time.
That’s far too deeply discharged. If the battery is well balanced at 54.9 V, the cells will drift apart as it discharges. The BMS will then shut down because one cell is below its minimum voltage.
There are electronics that stay alive even when the system is off. Otherwise how does it know to switch back on?
Raise the cut off higher to compensate for the draw it is the only way.
The only other way is a contactor on the DC side but even that will need a clever way to re energise to re engage like a mains detector. But tricky as you want it energised sometimes when there is no power
Thanks for the information.
A module to keep the charging infrastructure running, mounted on a toll gantry or mast and adapted to its surroundings, can’t be that much of a problem, surely. Or a small vertical-axis wind turbine and a solar panel.
Have a word with amateur radio operators about putting one or two emergency communications or other repeater stations on the gantry. Give the operators systematic support and free rein, and you’ll have emergency power to spare.
Well, the way I see it, if even such a marginal power draw is already a problem, you should consider using larger batteries and keeping more capacity in reserve at the lower end, because even the BMS needs power. For situations like this, I keep at least 30 per cent battery capacity available to keep the system running; the GX device needs power too, and so on. Otherwise, you could simply make sure you have a proper power supply and grid monitoring or automatic grid reconnection—for example, Siemens make RCDs and all sorts of things that you can switch back on remotely. Of course, the rest of the grid monitoring has to be compatible too. And if it’s a UPS system, how long does the whole thing run for? And why is the equipment even running on 220 V? Wouldn’t a 24 V/12 V backup solution perhaps be the better option? Then you don’t immediately lose 20 per cent!
I understad the idea of external backup like turbine/PV but unfortunately this is not possible. We dont have even BMS, cerbo or BP installed we have only Multiplus & batteries thats all (business decision which i cant change at the moment as the sites are already installed). The scenario when MP is left in ON state withut external ACIN power and it deeply discharge batt. is not usual, it happened few times because site construction delyas and mistake that engineer left MP in ON state. But, it shows one potentional problem and i think it will be good to have some simple solution to prevent batt. damage.
The solution can be only inside the cabinet where MP is located, not outside and it shloud be easy to install. So my idea is:
A) Power-OFF relay, it will be connected to battery, measuring its voltage, once it drops little bit under Cuttof (which is 43V so like 42V) it will disconnect the remote contact on MP.
B) Blackout recovery: Use AC relay on ACIN, on this relay will not see 230V it will disconnect the remote contact on MP. At this moment there is no consumption.
Once 230V ACIN will be restored, AC relay will again connect remote contact on MP, this will turn on MP, MP will measure battery voltage and start charging it, once batt voltage raise above 42V also DC relay will tur on (connect) and be ready to hold for case ACIN will again dissapear.
I think this could be elegant solution, no need dramatically install something expensive or not allowed by project. Also it is like plug and play solution.
What do you mean ? do you see some problems, or ideas ?
The problem is that any external relay solution also needs power.
This would have to be controlled via the BMS.
E.g. https://www.rec-bms.com/
And a suitable relay Bistabiler Relais-Treiber BSRD mit Relais BSR 750 LMP 12V/250A, 139,90 €, both with the appropriate voltage
The ralays do need power i agree but only in case they need switch to connect state, if no power on both relay the relays will disconnect which is actually what we want. Once power will come they will connect remote contact and “power on” the multiplus. So no power for relay is not problem in this case.
To sum up final solution:
In the end i did really easy solution, maybe somenone can benefit from this so i will share it.
A) I connected alarm contacts (from programmable relay) to the remote and set condition to keep connected when DC is above 43V and disconnect (defatult state) when DC is below 43V → this ensure batteries are disconnected from load and what is more important - from Multiplus consumption when standby (25mA) so the consumption dropped from 25mA to 2mA.
B) I installed AC relay and connected the NO contacts to remote contacts (in parallel with alarm relay) so when there is ACIN 230V it will turn MP on and batteries could be charged.
I tested this few times and it works great, advantage is that in cases batteries are drained to 43V and for whatever reason they cant be charged (falut, other consequences) they will last much longer in this state (2mA) than normally (25mA).
we can lock / close this thread as solved