Prevent battery discharge

Is there a way to prevent the battery from discharging without affecting anything else?

For context: I have a standard ESS. All the loads are connected downstream of the battery inverter. When the sauna is switched on, an extra 8 kW is drawn from the battery. I’m currently using the SOC slider to “hold” the discharge.

Can I disable discharging completely? The “inverter power limit” regulates the output, so that’s not an option.

It doesn’t need to be dynamic. When the sauna heater isn’t running, the rest of the house can draw power from the grid.

In the long term, the sauna is meant to be rewired, but that can’t happen overnight.

You can set the system (soft) switch to charge only, that will passthrough grid.
ESS is intended for self-consumption from the battery while above the minimum soc, so you’re trying to make ESS behave in a way it isn’t intended to.
You’d be better off putting the sauna in-front of the inverter on AC in, using a grid-meter, then you have some additional controls for the inverter back-feeding to cover those loads.

Use scheduled charge and only allow loads to run from PV only in the configuration

Otherwise a smart switch/ energy meter can be used then a node red flow that automatically freezes the SOC and releases the freeze when it is off.
It doesn’t necessarily need to be rewired just monitoring separate would help

One idea would be to use the control inputs for the §14a limit for this (feed-in restriction).

You could also set something up with a Shelly and Node-RED.

For any of these options, though, you’d need a control signal indicating that the sauna heater is on, to trigger the shutdown/limitation.

Thanks very much for the replies.

To sum up, there’s a meter on the supply line to the sauna heater. So I can tell exactly when the heater is on or off.

The aim was that, when I flip a switch “x”, everything stays as it is, except that the power comes from the grid rather than the battery. If there’s a PV surplus during that time, it should either be “offset” or go into the battery.

But from what I can gather, that probably won’t work.

You can emulate that via nodered, it can provide the switch then you need the logic to set the inverter limit to 0 watts until you’re done.

You can create a virtual switch that shows up in Cerbo and VRM.

Well, it’s not quite that simple :wink:

And ultimately, it makes no difference whether the battery runs flat powering the other loads or the sauna heater.

I once built a Node-RED flow that limits the inverter output depending on the SOC.