Charging a battery with a MultiPlus-II in off-grid mode

Question about the MultiPlus II — I’m new here. My system (3.6 kWp, SmartSolar 250|100-Tr VE.Can, MultiPlus-II 48/3000/35-32, 48V AGM battery bank with 4 x 60Ah) runs in off-grid mode. I want to keep it that way.

Now I’ve run into the classic PV problem: not enough sun, but the battery is empty. Can I use the MultiPlus II to recharge the battery without activating the internal transfer switch? According to the schematic, when voltage is present at AC IN, the transfer switch directly connects it to AC OUT 1. So the load — or the inverter output — is connected to AC IN.

So really, the question is whether the charger and inverter in the MultiPlus II can be operated independently of each other?

In short

AC IN ↔ AC OUT 1 : Not wanted

AC IN → DC → AC OUT ( without AC coupling ) : wanted

The alternative would be a separate external 48V charger. :

Hello @DB9DH,

I’m guessing from your nickname that it’s an amateur radio callsign.

When mains power is present, the MultiPlus switches through to the output virtually without interruption (within a few milliseconds) and charges the batteries. There are quite a few parameters you can use to control and influence this.

The switch at the bottom right of the unit lets you select charger-only or inverter operation.

Why don’t you want to connect AC in to AC out?

Do you have a GX device or a SmartShunt in your setup?

That gives you access to many more functions.

From what I can tell from your post, only the voltage is being used to determine the SOC.

There’s room to improve that :wink:

DB9DH doesn’t seem to be a valid callsign per QRZ.com. @DirkW are you a ham? I am K8MEJ, if anyone cares. LOL.

The OP didn’t tell us how large his genset is. Maybe he’s worried about it being too small to satisfy the AC loads in pass-thru mode and still have enough left to charge the batteries?

@DB9DH What is the size of the generator you want to use? Switching the inverter into charge-only mode every time you want to top up the batteries isn’t ideal, either, because you are then limited to the AC output of the generator. If you have a brief AC load larger than the generator output you will stall it. With the Multi in “On” mode, PowerAssist will augment the generator output with inverter output to satisfy that brief load.

You can find the callsign in an official German directory :slight_smile:

To really be able to help, we need more information from @DB9DH

That’s weird that QRZ didn’t have it. I assume you are a ham, too? You don’t have to out yourself in public with your callsign. I’m just curious. It might be fun to set up a sked sometime from Ohio to your QTH sometime if you’re up for it. My HF antenna at home has been broken for a while, however, so I’d need to get that fixed first.

Hi Ed, I don’t have an amateur radio licence :wink:

But thanks for the suggestion…

Another ham here! 73 de VA3HG Colin

@Buzzy , @OGPS am I allowed to keep posting here without a licence :wink: ?

All, yes I am a Radio Amateur. Nevertheless since long time not active.

Back to the “problem”

My system is an off-grid system, not connected to the GRID and with no generator either. 6 x 610W PV modules, so 3.66kWp, with a MultiPlus and solar charge controller as described. Plus 4 Victron 60Ah Super Cycle AGM batteries connected in series. So 48V, 2.88kWh.

Connected to it are two continuous loads totalling 100W and a switchable 350W load. But on dark days like today, it only supplies the continuous loads and can no longer recharge the battery, which was discharged to 50% during the previous night, in time for the next night.

The battery will be changed to an 8kWh lithium battery, and the number of modules increased to 22, but not until next year. In the meantime, I’d like to charge the batteries with a “normal” 48V charger on these rare occasions. The MP II has a 48V charger … However, in the MP block diagram, it’s located after (!) the transfer switch. I can’t use it like that, because if I connect the GRID to AC IN, it’s no longer an off-grid system, since the transfer switch feeds AC IN back to AC OUT. That won’t work; the system would then have to be registered …

I’d already considered configuring the MP for the rare occasion as “Charger Only” — that might work. The problem is that one of the continuous loads doesn’t handle power interruptions very well. The connection from the GRID to the MP II would need to be set up on a “break before make” basis :upside_down_face:

Hello everyone,

I have a similar problem/question, but with a generator on the AC input. In future, I’d like to run a PV inverter on AC out 1 of my MultiPlus II 48/3000. During extended power cuts, I’d like to be able to run an inverter generator on the AC input to charge the battery if needed.

My problem is that, with the transfer relay closed, excess energy could potentially flow back into the generator. Is there a way to prevent this through the configuration, without installing an additional electrical interlock?

Best regards,

Ralf

Once again, a quick question. Can I configure the MultiPlus-II 48/3000/35-32 to use the internal 48V charger without passing the mains from AC In through to AC Out 1—in other words, with the transfer switch remaining open? The inverter must not feed power back into the grid.

If not, I’ll have to use an external 48V charger, such as the Victron Smart IP43 charger, which would set me back about €350. I was hoping to avoid spending that …

If it’s charging, it would be pulling power from the grid, not backfeeding. But why can’t you just set the MPII grid mode to “None”, which always prevents backfeeding to the grid? Is there another source of AC other than the MPII?

As you yourself already pointed out in your original request, closing the AC IN relays connects the input to the output.
There’s no other way, because the same components are used for charging and discharging; the charger and inverter are not separate.

@DB9DH

An AC source can be connected to AC_out if its output can be regulated by frequency. When the battery is full, the MP2 raises the grid frequency to throttle the source. This is configured using the PV Assistant in VeConfigure.
Examples include microinverters or generators with the appropriate control system.

Otherwise, the cheapest option is a TelKo PSU from eBay (€100) to charge the battery.

“Normal” for an off-grid system would be a generator on AC_in without a Grid Code.

Where does the energy to charge the battery come from if it’s neither the grid nor solar?

Many thanks, that was the answer I was waiting for—not :grin:—.

AC in and AC out must remain galvanically isolated!

So the only thing that will help here is an external 48V charger, such as a Victron.

@BjoernK The only energy source is solar; there’s no generator. As the solar capacity is currently too small, the battery is not recharged in rare cases. In this situation, I wanted to charge the battery from the mains, galvanically isolated from AC out. The solar array will be expanded in spring.

It’s pretty wild how much solar and battery capacity you need just to run a continuous load of up to 200W (fridge, heating) reliably (!) without mains or a generator. The system will be expanded in spring from 3.66kWp to around 14kWp. In other words, I need around 14m² of effective solar area—which means 60m² in reality—to get 350W of output at 25W/m² of global irradiance.

At this point, it’ll only work with a separate external 48V charger, such as the Victron Smart Charger 48V. It may be possible to control it via the Cerbo GX.

Many thanks, everyone!

Take a look at telecom PSUs, e.g. Huawei or Eltek FlatPack 2. You can get them for 100 EIR on eBay.
You can switch them via a contactor using the Cerbo.

At least for the Eltek, there are ESP projects on GitHub that can control the PSU via MQTT over CAN.

I’m of the opinion that the Skylla chargers can’t be controlled (DVCC). You’ll have to check.

In the worst case, a 60V/5A bench power supply for 30 EUR from the big A would also work. I used that for charging without Victron.

Have you considered switching off the MP2 and powering the IT equipment via a DC-DC converter? I’m considering that for my UniFi setup. It runs entirely over PoE, and I’d only need to power the core switch and the gateway with 54V. A MeanWell DDR-240C-48 would be ideal. I already have DDR-60L-12s running for my fans.

Hi @DB9DH,

I have an installation similar to yours. For when my batteries run down, I have a manual Transfer Switch to switch the house loads over to mains power until the sun comes back.

My question, after reading your post, is whether I’m meeting the requirements for an off-grid system by having both mains and inverter cables connected to the TS. I understand that I am, since the transfer switch has no internal connection to neutral, and to switch from one to the other, the switch first passes through an off position with neither supply connected.

I’m asking you because reading your post made me wonder, and your installation seems to have the same kind of isolation as mine.

Thanks in advance,

Regards,

I had already thought of that too, using a 4-pole changeover switch. To be honest, I don’t know the answer.

“Actually”, it shouldn’t be a problem, since only the input for the load is being switched.

What absolutely must be prevented in this configuration is the inverter output being switched onto the grid; feeding electricity into the grid MUST be prevented galvanically in any case.

But I can imagine that the grid operator and the like might see it differently …

@DB9DH

Power is only fed into the grid if you have a Gridcode and the ESS Assistant installed. In all other operating modes, power is only ever drawn/consumed.

In my opinion, your choice of words, “galvanic isolation”, is incorrect, since even an isolation transformer wouldn’t prevent you from feeding power into the grid if power is fed into AC out and the batteries are full.

You’d be best off building yourself a test setup and trying out all the options.