Hello everyone, I’m a beginner and hope someone can help me.
I have a system of just under 50 kWp, with two SolarEdge inverters.
A battery system of 5 × 5 kWh (Pytes E-Box 48100R) is connected via three MultiPlus II units (one for each phase).
Each of the five batteries is connected to the MultiPlus by its own cable.
I’d like to expand the system by at least five units.
Can I simply connect another battery to each existing one using the available connecting cables, or does anything else need to be configured?
I’d be very grateful for any expert advice on this.
Unfortunately, the company that installed my system has gone insolvent, so I’m desperately looking for a qualified specialist company. I’d really appreciate any help with that, too.
Do you have documentation like a detailed list of equipment, a schematic wiring diagram and photos of your setup? That will be necessary for anyone to assist. It usually would have been provided by the previous installer.
You can’t just add batteries. The system needs to be properly configured. At a minimum, the battery capacity information has to be updated, all batteries brought up to the same voltage before connection, and the data communication between the master battery and the new additions has to be set. It’s also a good time to validate the health of the old batteries, and make changes to retire the old ones or swap a weak one.
Hopefully your new installer will get everything sorted. It sounds like good equipment was installed previously.
Bus bar… Use a single bus bar to connect everything DC
This is not how it should be done. And one battery on each phase is there batteries where are the two extras connected?
Do not build systems with separated batteries on multiple (separated) DC bus structures connected to subsets of the Multi/Quattro units in the cluster. This will not work.
These two do not belong together in any sentence related to solar. Get some professional help.
According to this, up to 16 units can be connected in parallel. If the existing 5 batteries are each connected individually to a busbar, there’s nothing to stop you connecting another one in parallel. The page also has some PDFs with technical specifications and instructions, so have a look there.
I have no experience with Pytes batteries, but according to the instructions, the communication protocol is set using the DIP switch on the front. So it should be set to the same value on all the batteries — zero (all switches down) for Victron, according to https://www.panda-solar.de/images/Datenblaetter/Pytes%20DIP.pdf
Unfortunately, I don’t have time for any training courses, although I’m very interested in the subject. Ideally, I’d get some good, expert advice from the community, or help from an installer.
Probably not. However, before connecting them in parallel, the new batteries should have roughly the same voltage as the new ones. Then switch off the MultiPlus units, switch off all the batteries, connect them in parallel and extend the communication cable to the new batteries. If the batteries behave like my Pylontechs, no further configuration should be needed. Then switch them back on one by one and finally reactivate the MultiPlus units.
It’s best to read the battery manual again beforehand; I don’t have any first-hand experience with them!
You can check the cable cross-sections, but it shouldn’t really be necessary if the system has been working so far without anything getting excessively hot. The additional batteries won’t increase the operating currents; they’ll only increase the possible operating time.
That’s not true! Yes, more operating time, but charging currents can definitely be larger as there are more batteries to charge, and they have more potential to discharge.
They could be larger if the demand were larger, but the existing 5 batteries can already deliver 100A each, thus 500A in total. I don’t know the size of the MP2, but the usual 5k is limited to 70A charging or 100A discharging. 300A max, and those would already go over the existing cabling. Hence my assessment that the cabling should be okay. Fusing might be another matter, though.
You can start by testing with one, but then you’ll be switching the system on and off more often.
The best way to equalise them is to measure the voltage of the new batteries, then charge or discharge the existing system until the voltage is within plus or minus 1 V of the same level. There will still be an equalisation current when you switch it on, but it will remain at a harmless level.
Either connect the new batteries directly to the DC busbar, or make groups of two batteries in parallel. Connect these “diagonally”: connect the positive terminal of one battery and the negative terminal of the other to the busbar. Connect the positive and negative terminals of the two batteries to each other.
It goes without saying that the DC fuses must still be suitable for the cables. If the Pytes batteries can provide enough current for the 3x MP2 ??? today, then we’re only talking about expanding capacity, and the cables can stay as they are. If the load is increased, the connections/terminals need to be checked. Amperol, for example, can usually handle 100A.
The batteries’ BMSs need to be connected, usually via CAN bus using RJ45/Cat5 cables, with the batteries configured with the appropriate addresses.
The batteries must, of course, have the same cell chemistry and number of cells. That should be the case if they’re from the same manufacturer.
There are different schools of thought about the voltage or SOC at which the batteries should be connected.
A) At 60% SOC, since this is in the flat part of the charging curve and the voltage difference is small, provided the SOC is estimated accurately by cBMD.
B) At around 3.45V/cell, since this is in the steep part of the charging curve and the difference in state of charge is small.
In both cases, the entire battery bank must then be kept at 100% SOC for long enough to allow the balancers to perform “top balancing”.
I’ve seen balancing currents of around 10–20A with my 15kWh/16s batteries. With an active NEEY-4A balancer, it took about 1–2 hours until everything was OK. I don’t know how the Pytes batteries work.
You can even connect batteries of different capacities in parallel.
That tip is really helpful. I just don’t know how to handle it.
The new cells will presumably have a low charge.
I won’t know how much, though, will I? Does that mean I have to match the old cells to a charge level I don’t know? Have I understood that correctly? If so, how is that supposed to work?