Battery now only discharges to 50 percent

Hello everyone

My MultiPlus II /3000 has worked perfectly with my 10 kW battery for three years. But now, all of a sudden, the battery stops discharging at around 50%. It won’t discharge any further. The discharge setting in ESS is at 10%, with 0 watts as the grid setpoint. It was working fine until a few days ago. Not any more. I control the battery’s discharge at night via Node-RED. What could be causing this? I’m stumped…

As is often the case, a bit more information about the system is missing.
Components installed?
Settings?
Screenshots?

Hello PKE,

I may have a lead for you, but please bear in mind that I’m a beginner, so my knowledge is limited.

I just want to share an experience I had a few days ago with limited battery discharge. Please bear in mind that my equipment is different from yours. I posted an article about the problem I encountered. You can read it online.

In short: incorrect instance configuration across my different devices (MUltiRS, Cerbo GX, and the batteries’ BMS) meant that the multiRS was calculating the battery charge theoretically, while the Cerbo GX and the batteries’ BMS were providing the actual battery state-of-charge values. Since the calculation made by the MultiRS was quite pessimistic (it showed a charge level of 30% when the batteries were actually charged to 100%), it would stop discharging the batteries as soon as its calculation showed that they had reached 20% charge (the SOC set as the threshold for stopping battery discharge). So when the MultiRS stopped discharging the batteries, thinking they had only 20% charge left, they actually still had 90% charge …

Once all three devices were set to the same instance number, the MultiRS synced with the figures provided by the batteries’ BMS to the CerboGX, and the problem was resolved.

I hope sharing this experience helps you solve your problem.

Kind regards.

The RS is completely different to the vebus inverters, the scenario you describe does not really apply here.
More likely an issue with active SOC or other thresholds being hit, but there is way too little detail to make an informed thumb-suck.

Thanks, here are some details

The settings have always been like this … I only changed the minimum SOC from 20 to 10

In August, the values were still OK. The battery dropped back to about 20% (I had set this as the minimum value). Since then, though, the discharge limit has gradually risen to around 50% by today. Another thing I’ve noticed … there’s no PV yield any more … is that connected? Or what’s causing the problem?

Thanks

What version are you using?
What battery monitor is selected in GX system settings?
Show a screenshot from the remote console when this happens - are there any ESS codes shown, what is the inverter state?

You should check your ess assistant dynamic cutoff thresholds, and other inverter limits and compare to the battery voltage to confirm if you are hitting any limits.
Disable any flows in case something has crept in there, always eliminate customisations from the equation.

Thanks. Switched off Node-RED, restarted the system, updated to the latest version, v3.81, and reconnected the inverter (it had dropped out at the end of August; only just noticed… I’ll fully charge the battery over the next few days. Then we’ll see…

I’d also check the voltage difference between the cells when the problem occurs. This can also cause problems if the difference is too high. However, you can only see this directly if the battery is connected via CAN bus (Battery Details). Otherwise, the manufacturer may have a tool for this.