Self-sufficient system with opportunity loads & Node-RED

Hello everyone,

I’m new to the forum, but I’ve already built several Victron systems: two in our expedition trucks, one at my children’s home, and now our own system, which I’d like to introduce here.

The setup

Since March 2026, we’ve been living in the south of France, where we bought an off-grid house in the forest. We want our house to operate independently while still being a comfortable, modern place to live. To achieve that, I’m bringing together solar power, stored energy, well water and two heat sources in a shared infrastructure.

Electricity is the foundation. Without a reliable power supply, the well pump at a depth of 80 metres, filling the water storage tank and automated heat distribution would all grind to a halt. So our journey towards self-sufficiency starts with photovoltaics, battery storage and a three-phase supply. The system is intended to support our daily lives—from lighting and the kitchen to the workshop and water supply, as well as electric mobility.

Energy is deliberately allocated. Supplying the house comes first; the battery takes priority over loads that can be shifted. The electric car and immersion heaters in the heating buffer tank use power when the energy situation allows. Victron coordinates energy-related permissions through Opportunity Loads, while Node-RED brings together local conditions and user control. This means large loads aren’t simply switched on all at once, but are coordinated with one another.

The water supply starts at the well, which is around 80 metres deep. A pump sends water to the storage tank; level measurement and control handle automatic refilling. The storage tank decouples daily water use from individual pump cycles. This is especially valuable when the available energy fluctuates throughout the day.

Heat comes from solar power and wood from our own forest. Three electric heating stages, with a combined output of 3 kW, can store surplus energy as heat in a buffer tank. This winter, I’ll see whether adding a second immersion heater, rated at a further 3 × 1 kW, would make sense. The wood-burning stove with a water jacket provides a second heat source. The heating circuit pump distributes the stored heat. The electric heating stages are only allowed to operate when energy is authorised by Victron and the temperature conditions are approved by Node-RED.

The house came with a single-phase solar system, a Victron inverter and a lead-gel battery bank. Let’s just say the setup had been put together in a very “laissez-faire” manner. No, actually, it was more of a fire hazard in the middle of the forest.

So I planned our three-phase off-grid system, trying to make sensible use of the existing components.

Following a fault in the existing system, on 30 August 2026 I switched the running supply over to the new system in just four hours—in the evening, by headlamp. To do this, I ran a 5G4 supply cable across the apartment from the new system to the old sub-distribution board. The Pylontech batteries were full, but the PV modules hadn’t been connected yet.

Because this emergency changeover was brought forward so drastically, I naturally still have a heap of work left to do. But for now, we’re well supplied.

Among other things, the main battery switches arrived last week. None of the 29 solar modules is at its planned mounting location yet; six are still on the pallet. Even so, with the 23 connected modules, we managed to harvest 34 kWh of sunshine on 21 October 2026, after three days that felt like a solar eclipse.

Since the system operates without feeding power into the grid, the setup is tailored to our own needs: provide reliable power, maintain reserves and shift usable surplus to mobility or heating.

In winter, the main consideration is the low sun. Module arrays facing south and mounted at an angle of about 60° should improve yield at this time of year. I’m currently preparing the site so I can install the solar modules in their final location and connect all 29 modules.

The last debugging run was successful, apart from one swapped phase assignment. I’ll leave logging enabled for the next few days to check that the system remains stable over time. After that, I’ll disable logging but keep the diagnostic function available for future analysis.

Once we’ve got through the first year of operation, we’ll decide whether we need more PV modules or more battery storage. I’d also like to experiment with a sand bunker to store summer heat for the winter.

The equipment

  • Four strings with a total of 29 modules and 12.06 kWp:
  • GAK 7899: PV surge protection for four strings, 32 A, 500 V
  • 1 × MPPT 150/60
  • 1 × MPPT 250/70
  • 1 × RS 450/100
  • 3 × Lynx Distributor
  • 1 × Lynx Shunt
  • 1 × Lynx Power In
  • 8 × Pylontech US5000 with a combined nominal capacity of 38.4 kWh
  • 3 × MultiPlus 48/8000
  • 1 × Victron EV Charging Station
  • Cerbo GX MK2 with Venus OS Large 3.85

There’s also a MultiPlus 48/5000 acting as a satellite on L2 of the three-phase system. Its AC input is limited to 6 A. Via PowerAssist/Peak Shaving, it helps supply power from the old lead-gel battery bank. This switchable branch provides a local energy reserve of around 7 kWh net if there’s a PV shortfall or a fault in the three-phase system.

Speaking of energy reserves: since we have no mains electricity, water or telephone connection here, electricity is the backbone of our entire infrastructure for power, water, heat and cooling. That’s why we have a multi-stage plan to preserve battery charge.

  1. Reduce electricity consumption
  2. Disconnect the satellite
  3. Charge the house battery using the LiFePo4 capacity of the expedition trucks (18.24 kWh in total)
  4. Charge the house battery using the old lead-gel bank (14 kWh net remaining)
  5. Use the small generator (single-phase, 1200 W continuous)
  6. Use the large generator, 3 × 2.2 kW

So we have 70.64 kWh of battery storage—with conversion losses, of course—before we have to call on a generator.

Remaining work

  • Install the winter arrays/remaining modules; mount the modules at their final location
  • Finish the MPPT aluminium plate/air duct; monitor temperature behaviour.
  • Install the ventilation and temperature control for the technical room/MPPT, program it and create a browser-based control panel
  • Install the 4 main battery switches
  • Finish the natural-stone well house and migrate the well pump control from “lab mode” to production, as well as complete the final installation of the Victron EVCS Station
  • Once the electric car has been delivered – test EVCS Loads VS well pump control
  • Continue developing the HMI debug page, incl. alerts to my phone
  • Bury the earthing strip for the house system (once our excavator arrives)
  • By summer 2027 – install air conditioning via OPL Loads

Node-RED and Opportunity Loads

Victron Opportunity Loads is up and running, deciding how energy is used by flexible loads.

The EVCS is controlled natively by Victron. The well controller reads the EVCS status and locks out the three-phase well pump while EV charging is active or the charging status is unknown.

For the heating stages, Victron sends the energy-related ON/OFF instructions via S2. Node-RED determines the heat demand based on temperatures, setpoint, heating day and protection conditions. The system decides whether it is a heating day based on the outside temperature at 03:30 at night.

The heating stages are only allowed to run when there is both a heat demand and a corresponding ON instruction from Victron. If the heat demand goes away, Node-RED switches off the heating stages and reports this back to Victron accordingly.

I currently have nine flow tabs in use in Node-RED, plus the system-generated empty flow:

  1. System dashboard
    Map and system overview, central telemetry, weather and additional GX.
  2. Debug dashboard
    Well debug chain and permanent heating fault display.
  3. Heating 1 – Immersion heaters
    Three S2 resources and heating channel controllers, as well as the central heating coordinator and settings storage.
  4. Heating 2 – Heating circuit pump
    Independent switching path for the heating circuit pump, with AUTO mode, timer and sensor protection.
  5. Heating 3 – Heating and cooling dashboard
    User interface, Shelly Pill telemetry and demand-based Pill polling.
  6. Water 1 – Well pump
    Well logic v1.5.4, sensor and operating mode evaluation, Hardware RevE and central system measurements.
  7. Lighting 1 – Outdoor lighting
    Shelly i4 operating modes and twilight signal; Shelly Mini01 as light actuators. The completed system is planned to have around 100 outdoor lights across the site, each with 2 W LED output.
  8. Graphics and files dashboard
    HTTP serving of images and graphics, without process control.
  9. Diagnostic file log
    Temporary, passive JSONL file logger for debugging; since performance fix 3.5.1, it has included hourly file rotation, a file list and downloads.

#Problem with troubleshooting and feature request for the Victron interface

While debugging my control prototype, I was missing an independent display of the current OPL decision.

Under “AC loads”, I can see the reported heating loads. However, I can’t tell from this whether Victron is still requesting that they run or whether my Node-RED control has kept an earlier ON state because of a fault.

“Opportunity Loads enabled” in the settings doesn’t answer this question either.

My request: a dedicated OPL status screen

The following information would be helpful:

· Overall status: OPL is actively regulating, paused or disabled, or has handed over control.

· For each load: current OPL instruction: ON, OFF or no active control.

· Reason for the decision: for example, insufficient surplus, battery charging priority, phase/inverter limit or minimum run time.

· Time of the last instruction.

· Separately alongside this: reported load state and power, preferably with an indication if a discrepancy persists.

Example:

Immersion heater L1
OPL instruction: OFF – insufficient surplus
Reported state: ON / 1,000 W
Note: Instruction and reported state do not match.

The key point would be for the displayed instruction to come directly from the OPL coordinator and be independent of the load’s reported state.

That would make it easy to distinguish during troubleshooting: is Victron actually still requesting the load, or is the problem in the connected control system?

Is this diagnostic option already available elsewhere? If not, I’d be pleased to see a status screen like this in the GX interface and Remote Console.

I’ll add photos later.

Best regards,
Philip

A very nice system and lots of good ideas in the control setup. I’m looking forward to the next instalment at the end of 2027.

I’d replace the immersion heaters with a domestic hot water heat pump. It saves electricity in winter and during the shoulder seasons, and dries out the plant room.

In the long run, I’d simplify the system and use just the one battery stack.

If you heat with wood, a water-heating wood-burning stove could make sense.

If the buffer tank isn’t large enough, you can add “phase shift material”.

Good luck, and have fun!

Thank you for the kind words and for thinking it through! :blush:

A domestic hot water heat pump isn’t an option for me, though: too expensive and unnecessarily complex for our setup. The immersion heaters run exclusively on opportunity loads and use the surplus that the off-grid system would otherwise have to curtail—we can’t feed electricity into the grid here. So the idea is to make sensible use of electricity we’d have anyway. If we don’t get enough from the PV system, I’d rather add a few more panels. With plenty of DIY work, the price of a heat pump would cover quite a bit of extra PV, including the mounting structure.

The main battery is already sized to see us through around five overcast days at our planned level of consumption. Fortunately, weather like that is rare here in the Var. Only after that would we use the batteries in the expedition trucks if needed, or start up the generator. The old lead-gel batteries are simply too good to throw away, given the capacity they have left. So they can keep doing the job described until they reach the end of their service life.

The water-heating fireplace is already installed and connected to the same buffer tank as the immersion heaters. It provides 14 kW to the water and 7 kW to the room.

I’m also taking a KIS approach to additional thermal storage—“keep it simple”: once our excavator has been delivered, I’d like to build a well-insulated sand bunker and charge it with heat over the summer. I’ve looked at a few DIY and professional projects and done some initial calculations for our situation. It’s on the project plan for 2028. We’ll see how much of that heat is actually usable seasonally—my aim is to significantly reduce our need for firewood.

So there’s still plenty to report before the end of 2027. And apparently, it’ll carry on after that … :wink:

Best wishes,

Philip