2 - Quattro 5000 in split phase with the grid input current set to 20A. To comply with local reg’s, I want to reduce that setting down to 16A. Using VE Bus system configurator and the Mk3 dongle connected to an unused port on one of the Quattro’s. Within a minute or two of connecting the dongle & opening the App, both Quattro’s shut down and causes me headaches. Is this normal behaviour?, and if so what are the next steps in setting the grid input max level?
What other components do you have in your system?
A GX device? A lithium battery with CAN-Bus communication?
I’ll add to what @M_Lange is going to suggest: I suspect you have a GX device and communicating batteries. Plug into shore power and the inverters won’t shut down when they loose BMS connectivity to the batteries. Then you can make your settings. You could also disable BMS control of the Quattros, but it’s easier to plug in if you can.
I have a Cerbo GX, and 1200AH worth of battery’s (48v). To get the devices running again, I powered down the Cerbo and then reconnected it. The JK BMS’s do control the system, but that makes me wonder why; when using the MK3 dongle with the app, the inverters shut down… So I should connect my Grid charging circuit first, then connect my Laptop to the Quattro’s via the dongle, then the VE Bus sysconfig App will work without shutting down the inverter/charger?
Thx
When the dongle is connected, there are 2 GX devices on the network.
This is problematic.