AC Thor 9S power: Why is the Cerbo unfortunately throttling the PV chargers?

Hello, does anyone have any ideas?
My system with two additional Fronius inverters is unfortunately throttling the output of the MPPs.

I’ve installed two My PV AC Thor 9S units, but the system throttles the output at 50.2 Hz, so the heating elements aren’t getting the full current.
Why is that?
I could upload a screenshot from the VRM portal, if only I knew how, …

To clarify,

Is your system throttling down DC coupled MPPTs and allowing the Fronius AC coupled inverters to supply to loads at 50.2Hz rather than allowing the full DC charge and increasing the frequency to throttle the AC coupled PV thus preventing the AC Thor from detecting that there is excess?

Jona

It would be interesting to see the settings for MultiPlus and AC-Thor.

Images or other data can be uploaded here:

That’s normal: when ACPV and DCPV are present, DCPV is curtailed first, in favour of a normal “50 Hz”, if possible.

You therefore shouldn’t control the MyPV via frequency control. It’s not a very sensible control mechanism, because even if, for example, the frequency were currently at 51.0 Hz and the MyPV started drawing power, that would only cause the frequency to drop again, just as the frequency-generating system decides that the ACPV no longer needs to be throttled — that is, as soon as the “small amount of wattage” has been fully used up.

We do this at our company, where we’re off-grid, using frequency alone, and it works brilliantly. However, we have the PV connected only via MPPTs.

You just need to match the frequency settings in the MultiPlus, AC-Thor and PV inverter.
The AC PV should only start being curtailed once the AC-Thor is running at 100% output.

That will probably be the crucial detail. With the default values, I see a “chicken-and-egg” problem: no increased frequency, no MyPv. No MyPV, no need to unthrottle DCPV if the existing ACPV covers the current demand sufficiently (with minimal throttling, at 50.2 Hz).

I can’t make sense of My PV.

I suspect the frequencies aren’t properly coordinated here. The AC Thor should simply increase its output earlier, or the AC inverter should throttle back later.

The frequency settings of the inverter assistant and the my-PV need to match.

Since we have several systems connected in series, the downstream systems effectively act as PV inverters, so frequency shifting works without any problems.
Otherwise, it’s also enough to simply add a balcony solar system to a setup like this to have PV generation on the AC side.

Details of our system

We have a main system in the office with 80 kWh of Pylontech, 3x MultiPlus 20k (until recently, 3x 10kVA) and, I think, around 20kWp across several MPPTs.
The warehouse/workshop is connected to the main system, with 75kWh of BYD, 3x MultiPlus 10kVA (until recently, 3x 8kVA) and, I think, around 15kWp across several MPPTs.
The individual offices are also connected to the main system, each with a small ESS.

We also have a CHP unit with around 5kW of electrical output in the system, whose waste heat is used to heat the hall a little in winter.

We’re currently expanding the system further.
Another 45kWp has been installed on the warehouse roof, of which around 14kWp is connected to the existing system in the hall via a 450/200.
The rest is going onto a new system with the HS19 and 75kWh Pytes HV.

A few pictures are on our Facebook page:
https://www.facebook.com/ServiceTeamDoebeln

Yes, unfortunately, that’s how it is.
AC-coupled inverters operate at 50.2 Hz, while the DC-side MPPTs are throttled and produce almost nothing.
Even if I reprogram the AC Thor to lower the frequency to 50 Hz, the MPPTs still produce hardly any power (100 W).

A “Share post” window opens for me, … ??? There’s nothing there where I can upload anything ???

In an off-grid system, it has to be controlled via frequency control, right?
MyPv specifies it that way.
I was surprised too, and had hoped there might be another option (Modbus, …), but even when I asked about this, the only answer I got two weeks ago was from Matthias L, who said that this is the only way to do it.

You first need to click Reply and then the icon.

As I’d already mentioned in your other topic, work is underway to control My-PV devices via Opportunity Loads. As far as I know, this would then be done via Modbus.
I can’t say when it will be publicly available.

I also asked My PV for their recommendation on the correct settings.
They replied: AcThor 1 50.1 Hz, -50.5 Hz; AcThor 2 50.5–51 Hz.
But what’s the point if the DC charge controllers are throttled back too early, presumably by the Cerbo?
In the mornings, it’s sometimes the other way around: the MPPTs supply the power, while the two Symo 6.0-3M units throttle down and only produce 30 W each.

Okay, got it now, ..
I’ll upload something tomorrow; it’s no use to anyone in the dark now, is it?

It should produce more when I set the ACThor to 50 Hz, but unfortunately it doesn’t!

What settings have you configured on the AC inverter and the assistant? AC THOR needs to increase its output BEFORE the AC inverter reduces its output. The AC inverter must not start reducing its output at that frequency until AC THOR is at 100%.

It’s about what you’ve configured, so it doesn’t matter whether it’s light or dark outside. :grinning_face:

With multiple AC Thor units, it’s naturally a bit more involved, as you have to set a priority through the settings.

If it’s not too urgent, I probably wouldn’t bother doing extensive testing at this point and would wait for the integration into Opportunity Loads.

Matthias,

This is a hot topic for me at the moment choosing whether to use relays/shellies and whether to program in Nodered or in OL.

Do you know is the AC Thor integration in Beta testing at the moment?

Thanks

It’s in internal testing currently, but the developer of that has a 2 week vaction now - so will take some time till it can be published. I’ll schedule him a slack message about the status for 7 am on his return day :innocent: