# AC Input current limit exceeded

**URL:** <https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306>\
**Category:** DIY\
**Created:** [6 February 2025 18:34 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306 "2025-02-06T18:34:12Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [6 February 2025 18:17 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/1 "2025-02-06T18:17:45Z")

</div>

I have the same problem.  
Only solution for now is using ac-out2 for powering the car charger and solar panels who needs to go off when grid fails.

If you put solar on ac-in and in the summer there is max. Delivery back in the grid (16A) + the inverter decides to feed in the grid with max capacity the main breaker trips also.

So it is not only a draw from grid problem but also an upcoming feed-in to the grid issue.

For people with reachable main breakers as a switch its not a real problem but in my case i have the old melting fuses so i need to call the network supplier (Stedin) who will charge me €650 per visit.

SOLVE THIS !

 ![20250206_191910](https://europe1.discourse-cdn.com/victron/original/2X/a/afa04151700e2edd300f9d57155b8891ceea0ac6.jpeg)

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [6 February 2025 18:34 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/2 "2025-02-06T18:34:12Z")

</div>

Are they fast blow slow blow?  
How much above the input limit is it feeding in?

> [@huib](#):
>
> Delivery back in the grid (16A) +

Is this the absolute limit? Has derating been factored in?

> [@huib](#):
>
> solar on ac-in and in the summer there is max.

So has to be controlled by a different method. What AC PV is it?

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [6 February 2025 19:51 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/3 "2025-02-06T19:51:25Z")

</div>

Why is this post split in 2 different ones? The problem is exactly the same as the first post starter mentioned… !  
The system is not peak shaving on the grid meter.

For me now it’s a hypothetical problem because i have put everything on ac-out

I have 3 phase mp2 -48-5000 with 20 kWh pylontech

Phase 2 and phase 3 has about 2500 wp per phase and only normal loads like washer and dryer and some air-conditioning

On phase 1 are the heaviest loads, 16A car charger, heat pump, 150L boiler and also the most solar yield. In total on phase 1 is 5670 wp solar. 3000 on AC-out1 and 2670 wp on AC-out2 (switches of in case of grid failure)

So theoretically i can feed in phase 1, 25A of solar and 17A of inverter power when the sun is fully shining and the inverter (for any unknown reason) is also feeding in the grid.

With my 3x25A main fuses (type C i guess) it is waiting to be blown when solar is on AC-OUT.

And then knowing i have bought the whole Victron system (€8700,-) for peak shaving purposes i am fairly disappointed the system is not protected by the VR3p75CT grid meter but everything needs to go through the inverter.

The result is also that my car is now draining the battery when the dynamic price are low because “battery used for critical loads only” also applies to AC-out2.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [7 February 2025 05:37 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/4 "2025-02-07T05:37:34Z")

</div>

> [@huib](#):
>
> The system is not peak shaving on the grid meter

This can be affected by settings and set up. So first that needs to be explored.  
Since your system is not the same as the other poster it is now a unique thread.

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 07:10 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/5 "2025-02-07T07:10:16Z")

</div>

No it is not a setup or settings issue. The problem is in the victron approach.

I have tried all possible settings several times.  
I have tried several posts on this forum about this same subject. I even emailed Harold Halewijn, a famous installer who put all his experience on YouTube and even he said this is a victron problem since venus os 3.30

The only important thing for a grid meter is to keep the import and export values as set in the system.

It should be fairly simple.  
It you say no more in or out than 25A and you have a grid meter than thats the limit.  
No exceptions.

If you say no feed in than thats the limit.

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 07:24 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/6 "2025-02-07T07:24:29Z")

</div>

It should be working like this.

1. If you have no victron system, just a power line with 10A breaker.  
If the boiler is on (6A) and the washer is pulling 8A during heating the main breaker trips.  
If you have solar coming in on the same line the load in the breaker stays within it’s limit.

 ![IMG-20250207-WA0000](https://europe1.discourse-cdn.com/victron/original/2X/0/0250b781327e36909a7f37ded02341d6d6a5ee4c.jpeg)

The victron system (with enough battery filled during the day) should be able to take this same task

 ![IMG-20250207-WA0001](https://europe1.discourse-cdn.com/victron/original/2X/b/b13993511fdcf2dfcf3d1dd4296df646a899984e.jpeg)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 07:27 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/7 "2025-02-07T07:27:16Z")

</div>

Peak shaving is what controls this, the system should also supply from battery above the input limit, provided the battery is above min soc, or there is solar.  
This requires ESS to be operational and loads to be on AC OUT only, not grid parallel.

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 07:31 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/8 "2025-02-07T07:31:35Z")

</div>

> [@nickdb](#):
>
> This requires ESS to be operational and loads to be on AC OUT only, not grid parallel.

And that’s the problem because if everything is on AC - out your car charger is draining the battery even if the dynamic power prices are low at that moment. Supply from battery (only critical loads) does not do what is said because loads on AC-OUT2 are not critical loads (they are disconnected when grid fails) but still be draining from battery!

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 07:34 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/9 "2025-02-07T07:34:17Z")

</div>

This is my situation

 ![IMG-20250207-WA0002](https://europe1.discourse-cdn.com/victron/original/2X/e/e14c4c86b9995b50cc57fa2268654451e3d2e94d.jpeg)

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 07:34 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/10 "2025-02-07T07:34:40Z")

</div>

AC2 can be forced on, there are assistants for that.  
AC PV introduces another variable into the equation.  
The system also has ramp times, so load can fluctuate, especially as larger ones are switched in/out.

Victron EV chargers are meant to have intelligence to restrict what they draw based on system state to prevent batteries being drained.

How are those other PV inverters being metered?

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 07:42 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/11 "2025-02-07T07:42:00Z")

</div>

The problem is inside the mp2 inverter.  
There is only 1 ct clamp measuring only the AC-IN. Because of that it cannot differentiate between loads on AC-out1 and AC-out2.

A grid meter and non critical loads on ac-in should be able to solve that issue but apparently it is not a priority to victron

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 07:44 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/12 "2025-02-07T07:44:23Z")

</div>

It’s more of a case that this wasn’t a use case when these systems were developed.  
You can add meters, but in the case of an EV charger, the Victron charger is accessible via modbus and sharing power information so the GX can control the charger as required, so it can typically be installed on AC OUT 1, or AC IN, if you don’t mind it going offline in an outage.

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 07:55 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/13 "2025-02-07T07:55:33Z")

</div>

The grid meter can do the same thing and not only for the car charger.  
It can take into account the boiler, heat pump, and car loads all at once.

Maybe there is a problem with the grid meter 3 phase regulating but it is giving loads per phase on vrm. So the information of the grid load or main breaker is available.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 07:59 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/14 "2025-02-07T07:59:32Z")

</div>

It’s hard to tell from your diagram. You have 3 sets of AC PV, but you show one meter at AC IN PV only, no external grid meter. If that is accurate, I don’t see how the system would actually know what energy is going where.

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 08:06 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/15 "2025-02-07T08:06:46Z")

</div>

I have no problem with the solar panels without a meter. They are all behind the inverter so that’s no problem.

Actually they are 6 sets in total with different brands of inverters and all measured by homewizzard but victron gx device can not see it.  
Victron can also not see every load after the inverter but is still able to establish a 0 to the meter in ess mode.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 08:21 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/16 "2025-02-07T08:21:37Z")

</div>

I suspect the issue here is you actually need an external grid meter, @lxonline can you confirm?

---

<div class="post-metadata">

**Author:** ![RikHa](https://avatars.discourse-cdn.com/v4/letter/r/d6d6ee/32.png) [@RikHa](https://community.victronenergy.com/u/RikHa)\
**Post date:** [7 February 2025 08:21 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/17 "2025-02-07T08:21:58Z")

</div>

Exactly what @nickdb says, how does the system know what is going on on the grid connection? And how does it know what both PV inverters on AC out are doing?

Btw; did you see the solution I wrote in my link?

> [@Exceeding grid limit despite limit set at 25A](https://community.victronenergy.com/t/exceeding-grid-limit-despite-limit-set-at-25a/21281/6):
>
> Hi LX, I’ve tried to set the limit om 10A as well. The system just doesn’t take the loads in front of the MP’s into account. When I put everything on ACout the peak shaving works flawless. Yes I did update everything to the latest versions. No beta. In the mean time I found this posting from @SmartVolt : [Grid current limit exceeded with DESS and peakshaving on - #3 by SmartVolt](https://community.victronenergy.com/t/grid-current-limit-exceeded-with-dess-and-peakshaving-on/1623/3) And indeed that seems to work. Only problem is that when you have only loads on ACin configured in system setup, you …

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 08:24 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/18 "2025-02-07T08:24:20Z")

</div>

The peak shaving update states that an external grid meter is needed for parallel loads, and you don’t have one.  
The system will not do the maths, and the PV meter is informational only.

---

<div class="post-metadata">

**Author:** ![huib](https://avatars.discourse-cdn.com/v4/letter/h/278dde/32.png) [@huib](https://community.victronenergy.com/u/huib)\
**Post date:** [7 February 2025 09:17 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/19 "2025-02-07T09:17:42Z")

</div>

I have the VR3P75CT measuring the grid.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [7 February 2025 09:18 UTC](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306/20 "2025-02-07T09:18:37Z")

</div>

On your diagram it is measuring the PV inverter only and should be on a PV inverter role.

[Next page](https://community.victronenergy.com/t/ac-input-current-limit-exceeded/21306.md?page=2)