I’m still new to Victron and have the following setup:
3 x MultiPlus-II 10000
1 x VM-3P75CT energy meter
1 x Cerbo GX MK2
8 x Pylontech Battery 5000
The Multis are connected straight after the mains connection, and the whole house load is connected to the output of the units.
Oh, and the solar system is a 25 kW SolarEdge, also connected to the house load. So during the day, when there’s more sun, the output shows 0 watts. It hasn’t been integrated into the Victron system yet, as I still need to look into that
So far, everything works during the day when the sun is shining: the batteries charge and the rest goes to the grid.
Now for the problem: as soon as no more power is being produced, the batteries start discharging, but the discharge rate then goes up to 20 kW and power is still being drawn from the grid!! (see photos) I really have no idea what’s going wrong. Under normal conditions, without the heat pump, the household consumption is around 2 kW for two families. Can anyone help me with the configuration?
In the last picture, I switched from bulk charging to manual inverter mode.
Morning, morning, Steck (Martin) and welcome to the Blue Hour forum …
First of all … a bold “first setup” with so much power on the AC side and the necessary batteries on the DC side …
Why not post a few pictures of the setup … distribution board, batteries, DC connections, etc. … you might be able to spot a few things from those.
Have you installed the ESS Assistant on all the Multis?
Are phases 1–3 assigned correctly, and do they match the VM’s measurement inputs, which need to be connected the RIGHT WAY ROUND?
What’s your ESS configuration like … you can post it here
A small diagram of the overall setup would be great … how and where is your current solar system connected … that’ll be helpful for metering and analysis later.
What mode is your ESS running in at the moment …
Let’s take it one step at a time … we’ll get there … the household is being supplied with power, after all. It may well be that everything will need to “restart” once the update has been installed … make sure to give the female members of the household a heads-up in good time
… do you have full access to your system? … and are you even able and allowed to change anything? Warranty issue
The connection from the batteries to the Lynx is really ridiculously long … up / across / and back down again. Any ordinary “DIYer” would keep the connection as short as possible … even if that meant running a cable across the sink. At the moment, that’s 4 m too much … so a good 8 m there and back
You can download your current VE Configure file via/in VRM … save it and then edit it if needed … Warranty issue again!!!
Yes, unfortunately there was no other way because of the space, but the cross-section is fine.
The switch is actually labelled incorrectly. It just switches between supplying the consumers directly (mains power) and supplying them via the Multiplus, so that if there’s a fault, the house can be supplied normally using mains power only.
Here’s the configuration. I hope it’s the right one. No, the batteries are charged via AC out 1, so from the house mains. The solar system is also connected to the household consumption.
The config looks OK so far. The batteries are charged via AC In from the mains. The Multi then acts as a charger … When the VM detects a surplus, the Multis should always feed it into the batteries, with consumption close to “0”.
What mode is the ESS in on the Remote Console? What is set for grid metering?
Where is that gigantic amount of consumption coming from after 7 pm … during the day, it could have been the PV system if the clamps were fitted the wrong way round … then feed-in would show as consumption … but after 7 pm ???
The VRM overview looks almost OK … the PV system is generating a surplus and the Multis are busy charging … BUT no consumption shown for the AC loads?
The “DC power” display could be removed from the overview … disable the DC loads display in the Remote Console. I assume that no external DC loads are being supplied.
Where is this enormous consumption after 7 pm coming from … during the day, it could have been the PV system if the clamps were the wrong way round … then feed-in would show as consumption … but after 7 pm??? That’s the problem: it’s coming from the battery; the house isn’t using that power. If I switch off the battery, with just the inverter running, the house only uses about 1.5–2 kW. As soon as it starts discharging, the AC load continually increases, and the menu then shows Bulk charging, even though power is being consumed!!
BUT no consumption shown under AC loads? That’s because the solar system is connected here, so it shows 0 as long as more power is being generated than consumed
So if the solar system is connected to the AC Out of the Multis, its output MUST be specified in the ESS assistant so that the GX can detect it and reduce it via a frequency increase in the event of a grid outage … better, of course, would be to have a separate measurement using a meter configured as “PV on AC Out”.
The mode should definitely be “Without BatteryLife” … But as long as nobody can check on the “cabinet”, sorting this out remotely will be difficult
Something here seems to have been wired and/or configured incorrectly …
It seems the new Victron distribution board was simply connected in front of the old main distribution board … take a look at the grid meter and see whether the readings for 1.8.0 and 2.8.0 match the Victron display.
If you open the config file mentioned above, you can access the ESS assistant over on the far left … But do it tomorrow, as the system will definitely restart!!! You can then enter the PV power at AC Out in the menus … The value is entered only in the ESS of the master and applies to the entire system across all 3 phases … The other ESS menus are pretty limited here anyway … but you’ll also need the VE.Bus System Configurator for that, since you have a 3-phase config. This is where you enter all 3 Multis … Right-click on the master and VE Config will open for the respective Multi … Exit and then save …