I’m in a weird situation, I have some knowledge and a bit of education in this field, but didn’t complete electric engineering college and I’m not a certified electrician so I’m not allowed to do 230V stuff myself. So, I’m aware I might be wrong and missing something, but I need a third or possible 4th, 5th, 6th person to confirm or disprove my suspicion to be sure.
I have a 3 Phase Setup with 3x MPII 10kva. Inverters are only connected via AC-In, no AC-Out. And AC coupled PV, but the PV doesn’t matter now.
Currently each phase and a combined neutral are going through a 40A 3P+N MCB.
My electrician just said he realized that was a mistake and now wants to swap that out and instead use a 1P+N 20A breaker for each Multiplus. He argues that, in the current setup, the MCB will trip earlier, because N will have higher current than 40A when multiple phases see unequal load. Also, the wiring can only take 60A so he can’t go higher than 3x20A. He still says that I’ll be able to draw more power that way than I’m currently able to do.
However, I’m pretty sure that the phase shift between those phases causes the current on N to balance eachother out to some degree, maybe not completely, due to uneven load, but at the very least it will never go above 40A(rms). I also did a LTspice simulation that confirmed that.
He says this is not a true 3 phase system so they don’t balance eachother out, but rather add up on N and that the spice simulation is wrong, but he doesn’t know how to simulate it correctly.
The easiest solution would be to test that, but we currently don’t have enough consumers in the house and are not allowed to export anything. Plus my whole house is behind a 40A breaker so I can’t even use the forced charging from grid to test it up to those 40A without risking to trip the main breaker. (I might be wrong here? can I test this somehow?)
Thus, I have currently no way to test those claims in practice, but the installation is mostly finished and they want to replace the breakers now, which I want to preven,t because I think that would be worse for me and I don’t want to realize that after we signed off on the install.
This is the current setup:
LS stands for breaker (LTspice doesn’t have the symbols for them) And here is a picture of it just to be sure:
So, which is correct?
3x Multiplus 10kva in 3 phase setup.
3x 1P+1N 20A breakers and break each neutral separately. (Neutral can only take 60A at most)
or 1x 3P+1N 40A MCB with shared Neutral going through the MCB.
Remember that it’s a 3 phase setup and they are shifted 120° each, which I believe to be the most important point here.
Thanks in advance!