Hi everyone,
I have a 3-phase Victron ESS. It was working good for last few years but lately I am having problems.
My system setup:
- 3 × Quattro 48/10000/140-2x100
- Cerbo GX
- Pylontech battery bank, 720 Ah
- ESS: Optimized without BatteryLife
- Multiphase regulation: Individual phase
- Grid setpoint: 10 W
- Grid metering: Inverter/Charger
- Grid code: Germany VDE-AR-N 4105:2018-11, external NS protection
- External anti-islanding protection: Ziehl UFR1001E
It isnt working reliable anymore now. First, a fuse in the grid supply to the Victron system failed. The system continued running from battery until Pylontech reached about 5% SOC, which is fine since that is what I have in my settings.
I then switched the house to a direct grid bypass so the ESS was no longer supplying the loads.
After replacing the failed grid-side fuse and switching back to the Victron system, I also found that the L2 fuse on the AC output from the Victron system to the house had failed. After replacing that fuse, power was restored on all phases.
Since this event, however, the L2 Quattro behaves differently from L1 and L3 when the grid is connected.
With the grid connected, L1 and L3 behave normally under ESS and supply their loads from the battery or from pv voltage if there is any, while L2 almost always just is in passthrough/grid import.
The “Inverter” LED on L1 and L3 flashes normally while ESS is discharging the battery. On L2 it hardly flashes at all when the grid is connected.
If I disconnect the grid completely, all three Quattros switch to inverter mode (L2 also).
So the L2 inverter is capable of producing AC power. The problem only appears during grid-connected ESS operation.
The L2 Quattro has also recently become very much louder than L1 and L3.
It produces a mechanical/rattling or “knattering” noise which can even occur in inverter mode at almost zero load. L1 and L3 to not make such noice.
I have a video recording where the noise can clearly be heard.
After disconnecting and reconnecting the grid, the complete 3-phase VE.Bus system has often refused to reconnect to the grid for a long time. When looking at the cerbo here it shows correct voltange and requency for all phases but “Active AC Input is on DISCONNECTED”
The external Ziehl UFR1001E looked normal and both K1/K2 relays were active.
A VE.Bus “System reset” did not solve this problem. I then manually switched all three Quattros to 0, waited, and switched them back on one after another. After this full hardware power cycle, the grid was accepted again.
What I did already:
- 3-phase VE.Bus System Configurator check: OK
- Physical switch on L2: position I / ON
- ESS Assistant installed on all three Quattros
- L2 and L3 ESS Assistant configuration is identical
- ESS Assistant parameters:
- LiFePO4 with external/CAN BMS
- Battery capacity 720 Ah
- Sustain voltage 48.0 V
- PowerAssist unchecked
- Lithium batteries checked
- Dynamic current limiter unchecked
- Storage mode unchecked
- Use AUX1 as disable FeedIn signal: unchecked
- ESS Relay test: Completed
- Pylontech CCL: 370 A
- Pylontech DCL: 370 A
- No relevant VE.Bus alarms
- Grid voltage/frequency normal on all three phases
- UFR1001E / external NS protection appears normal
- L2 successfully inverts when grid is removed
- A full hardware power cycle temporarily restores normal behaviour
I also downloaded the complete Remote VEConfigure configuration and compared the units. So far I have not found a configuration difference which would explain why L2 behaves differently from L3.
Any suggestions would be very welcome.