3 phase MultiPlus-II 48/10000 ESS limieted power in and output

Hello,

I recently upgrade from the MultiPlus-II 48/5000 to the MultiPlus-II 48/10000
But out put power is about the same it is stuck at around 15kw…
Also charging is to maxing out (see pictures)

Is it the temperature?!? But why would the old MultiPlus-II 48/5000 do 15kW
and now the MultiPlus-II 48/10000 does about the same…

battery is 190kWh so they can handle the load easy




You’ve configured 18 kW In and Out Power in DESS … the system is trying to match that.

I though that was the max grid connection?
So I increase that I;ll be oke. thx

I think this is my grid connection max power because when you press the Info button it gice this info:
with a 3x25A connection, that would mean 3x25A = 75A x 230V = 17kW