# 3-phase Multi RS Solar stuck in passthrough

**URL:** <https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156>\
**Category:** DIY\
**Tags:** 3-phase, cerbo\_gx, multi\_rs, diy\
**Created:** [6 August 2025 11:21 UTC](https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156 "2025-08-06T11:21:51Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![rhernaus](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/rhernaus/32/33202_2.png) [@rhernaus](https://community.victronenergy.com/u/rhernaus)\
**Post date:** [6 August 2025 11:21 UTC](https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156/1 "2025-08-06T11:21:51Z")

</div>

I have a Victron system with;

- 3x Multi RS Solar configured as three phase

- VM-3P75CT energy meter connection via VE.Can

- Cerbo GX Mk2

- 5x Pylontech US5000

Firmwares:

 ![Screenshot 2025-08-06 at 13.17.30](https://europe1.discourse-cdn.com/victron/original/3X/8/b/8ba2fe54ca0f721206c1c0e93518c315b68f3f5e.png)

The VM-3P75CT, Multi RS’s and Cerbo GX Mk2 are daisy chained on VE.Can with terminators on both ends. In the Cerbo all devices show up on VE.Can Port 1.

 ![Screenshot 2025-08-06 at 13.10.18](https://europe1.discourse-cdn.com/victron/original/3X/f/c/fcd716cb987d529cec8b4f9ab8e259cae6335641.png)  
 ![Screenshot 2025-08-06 at 13.10.40](https://europe1.discourse-cdn.com/victron/original/3X/e/8/e8adc9a633347f726d709e12ea128ffb022a4545.png)

The Pylontech is connected to the Cerbo GX VE.Can Port 2

 ![Screenshot 2025-08-06 at 13.10.53](https://europe1.discourse-cdn.com/victron/original/3X/4/0/4036ad4f1a19751c2697bf4ca4c6388b7f4a23e9.png)  
 ![Screenshot 2025-08-06 at 13.12.12](https://europe1.discourse-cdn.com/victron/original/3X/f/1/f1dd1e048dcdf70dc23e1fe218e5127ddd377d04.png)

The Multi RS’s are all configured the same like this. But they all have their own phase assigned.

 ![Screenshot 2025-08-06 at 13.13.24](https://europe1.discourse-cdn.com/victron/original/3X/e/2/e25f600fbef4ff9b75e9b1606917e77119f9b000.png)  
 ![Screenshot 2025-08-06 at 13.13.16](https://europe1.discourse-cdn.com/victron/original/3X/3/b/3bc24c4d46ad9a7f208cdd2c3a28ddb9e9898851.png)  
 ![Screenshot 2025-08-06 at 13.13.06](https://europe1.discourse-cdn.com/victron/original/3X/3/c/3c2384c6932f76f920524bf14e7612a7eea404b2.png)

The Multi RS’s connect to the grid succesfully and the ACIN1 relay closes. My loads connected to AC-OUT-1 are powered. I have a SolarEdge SE16k connected to AC-OUT-1 too.

 ![Screenshot 2025-08-06 at 13.15.26](https://europe1.discourse-cdn.com/victron/original/3X/f/f/ff383e65c2c0b31dcf76e09a81450a4dd943c1b4.png)

But for some reason the Inverters stay in Passthrough state. I can only see that on the physical displays.

 ![Screenshot 2025-08-06 at 13.21.26](https://europe1.discourse-cdn.com/victron/original/3X/f/5/f5e072769beb2f7c51dff546197b77aed9df2bb6.jpeg)  
 ![Screenshot 2025-08-06 at 13.21.18](https://europe1.discourse-cdn.com/victron/original/3X/9/1/914758825fe2a8b439f3af506cb7e14c87ef9726.jpeg)  
 ![Screenshot 2025-08-06 at 13.21.10](https://europe1.discourse-cdn.com/victron/original/3X/1/4/14bf6e3d2cea43f2d1544ac39c7d990e2eabec84.jpeg)

As far as i can tell i have followed the documentation correctly. Can somebody help me troubleshoot this issue?

Thanks!

---

<div class="post-metadata">

**Author:** ![rhernaus](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/rhernaus/32/33202_2.png) [@rhernaus](https://community.victronenergy.com/u/rhernaus)\
**Post date:** [6 August 2025 12:42 UTC](https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156/2 "2025-08-06T12:42:29Z")

</div>

In case it helps somebody else. When i set Minimum number of inverters to start to less than 3 the system started working.

 ![Screenshot 2025-08-06 at 14.41.38](https://europe1.discourse-cdn.com/victron/original/3X/b/c/bcbbe4ae9f3fe61a2a4e7eb9175b4b7a078dcbe6.png)

---

<div class="post-metadata">

**Author:** ![alexpescaru](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/alexpescaru/32/270_2.png) [@alexpescaru](https://community.victronenergy.com/u/alexpescaru)\
**Post date:** [6 August 2025 19:34 UTC](https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156/4 "2025-08-06T19:34:54Z")

</div>

> [@rhernaus](#):
>
> When i set Minimum number of inverters to start to less than 3 the system started working.

I wonder which is the logic in this… 🤨  
If one has a 3 phase system and want it to work **only and only** when all 3 inverters are online simultaneously, how do you set it?

LE:  
Now I see that the texting is a little bit confusing…  
**Minimum inverters to start** is referring to number of inverters that must be active per phase.  
But… Hmm… Multi RS cannot be parallelized…

---

<div class="post-metadata">

**Author:** ![Jelle](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/jelle/32/33287_2.png) [@Jelle](https://community.victronenergy.com/u/Jelle)\
**Post date:** [27 August 2025 06:57 UTC](https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156/5 "2025-08-27T06:57:07Z")

</div>

I also walked into this trap, I got stuck for days. Thanks to this post I am finally in business

---

<div class="post-metadata">

**Author:** ![system](https://europe1.discourse-cdn.com/victron/original/1X/21a9a7b5db7c6339715f993568736a7053199995.png) [@system](https://community.victronenergy.com/u/system)\
**Post date:** [10 September 2025 06:57 UTC](https://community.victronenergy.com/t/3-phase-multi-rs-solar-stuck-in-passthrough/42156/6 "2025-09-10T06:57:10Z")

</div>

This topic was automatically closed 14 days after the last reply. New replies are no longer allowed.