3.62 PowerAssist glitch?

I upgraded from 3.55 to 3.62 yesterday. On 30A shore power, current limit set to 26A. Useage went up to 50A and got overload message via VRM. I checked and it was only pulling 15A from grid and power assisting the remaining 35A.

In the inverter menu it showed a discrepancy that the multi’s input was 24A, but my energy meter & power watch dog disagreed.

I returned to previous OS 3.55 and no issues.

Is there something I can try to remedy this or is it a glitch in new version?

Can you confirm what GX you are using and if you have any grid/energy meters configured?

Im using a cerbo gx and Victron 3p75 emery meter

Is this perhaps due to the minimum power assist current?

That number differs per model inverter/charger

Her are some screenshots.



Battery current to show when assist kicked in.
Multiplus ac in showing 24-27 “false amps”
Grid meter showing actual input of only 15amps