# 2x Multiplus II 10KW in parallel single phase external transfer switch

**URL:** <https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827>\
**Category:** DIY\
**Tags:** parallel, multiplus-ii\
**Created:** [September 13, 2026, 7:01pm UTC](https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827 "2026-09-13T19:01:04Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![baccardi](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/baccardi/32/59051_2.png) [@baccardi](https://community.victronenergy.com/u/baccardi)\
**Post date:** [September 13, 2026, 7:01pm UTC](https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827/1 "2026-09-13T19:01:04Z")

</div>

Can I combine the master OUT-1, the Slave OUT-1 and the GRID on the Same busbar? My grid service is 60A 230V single phase. as recommended by victron for on three phase system for large inverter, I’m installing an external Contactor.

---

<div class="post-metadata">

**Author:** ![nickdb](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/nickdb/32/51440_2.png) [@nickdb](https://community.victronenergy.com/u/nickdb)\
**Post date:** [September 13, 2026, 7:02pm UTC](https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827/2 "2026-09-13T19:02:55Z")

</div>

Are you trying to connect AC IN and AC OUT on the same busbar?

---

<div class="post-metadata">

**Author:** ![baccardi](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/baccardi/32/59051_2.png) [@baccardi](https://community.victronenergy.com/u/baccardi)\
**Post date:** [September 13, 2026, 7:05pm UTC](https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827/3 "2026-09-13T19:05:30Z")

</div>

No only AC OUT 1 of both 10KW inverters plus the incoming grid.

---

<div class="post-metadata">

**Author:** ![lxonline](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/lxonline/32/25567_2.png) [@lxonline](https://community.victronenergy.com/u/lxonline)\
**Post date:** [September 13, 2026, 7:47pm UTC](https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827/6 "2026-09-13T19:47:27Z")

</div>

Did you notice that the grid and the output of the inverters has a contactor between them?

> **[6. Wiring diagrams - 6. Wiring diagrams](https://www.victronenergy.com/media/pg/MultiPlus-II_External_Transfer_Switch_application/en/wiring-diagrams.html#UUID-e2bfb6e2-2884-8f66-f3b3-8e637550872f)**
>
> An example of a general wiring diagram using MultiPlus-II units.

---

<div class="post-metadata">

**Author:** ![baccardi](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/baccardi/32/59051_2.png) [@baccardi](https://community.victronenergy.com/u/baccardi)\
**Post date:** [September 14, 2026, 2:10am UTC](https://community.victronenergy.com/t/2x-multiplus-ii-10kw-in-parallel-single-phase-external-transfer-switch/62827/7 "2026-09-14T02:10:09Z")

</div>

Yes, thank you for the update