Is it possible to use 2 x multiplus2 5000 on a 3 phase connection.

Ess is now running on 1 multiplus2 but i want to add a second one on phase 2.  
Now the multiplus2 is running on phase 1 and compensating for phase 2 and 3.  
i want to add one on phase 2,is that possible of can you only run 1 or 3 inverters?

If it is possible and i connect both inverters on the cerbo do i need to configure the second inverter as a phase 2 inverter? Or just connect them and finish?

The inverter is now only connected at the line in.

Thank you in advanced!

Richard

---

<div class="post-metadata">

**Author:** ![cmock](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@cmock](https://community.victronenergy.com/u/cmock)\
**Post date:** [24 January 2025 18:08 UTC](https://community.victronenergy.com/t/2-times-multiplus2-on-a-3-phase-connection/19843/2 "2025-01-24T18:08:02Z")

</div>

That’s possible, in VE.Bus System configurator you can select “dual phase 120” for this case.

---

<div class="post-metadata">

**Author:** ![Richard84](https://avatars.discourse-cdn.com/v4/letter/r/0ea827/32.png) [@Richard84](https://community.victronenergy.com/u/Richard84)\
**Post date:** [24 January 2025 19:09 UTC](https://community.victronenergy.com/t/2-times-multiplus2-on-a-3-phase-connection/19843/3 "2025-01-24T19:09:02Z")

</div>

Oke super, i thought so but there is not much to find for this configuration and i want to be shure.

Thank you for the awnser 😉

---

<div class="post-metadata">

**Author:** ![cmock](https://avatars.discourse-cdn.com/v4/letter/c/7c8e57/32.png) [@cmock](https://community.victronenergy.com/u/cmock)\
**Post date:** [24 January 2025 19:10 UTC](https://community.victronenergy.com/t/2-times-multiplus2-on-a-3-phase-connection/19843/4 "2025-01-24T19:10:09Z")

</div>

Yes, I also wondered what that was for, but then one of my 3 multis died and I asked here and learned about it…

---

<div class="post-metadata">

**Author:** ![Richard84](https://avatars.discourse-cdn.com/v4/letter/r/0ea827/32.png) [@Richard84](https://community.victronenergy.com/u/Richard84)\
**Post date:** [24 January 2025 20:53 UTC](https://community.victronenergy.com/t/2-times-multiplus2-on-a-3-phase-connection/19843/5 "2025-01-24T20:53:39Z")

</div>

Oke,

For me is it just for ess and keep 0 on the meter.  
8kw in total is enough for 99% of the time.  
Maby in the future i wil go for a 3rd 5kva but for now it is ok.  
But then i want first more power from the solar panels (it is now 6kw)  
Battery power is already a little more then 90kwh so thats more then enough.

It stays a build in progress 🤣🤣

---

<div class="post-metadata">

**Author:** ![owenb79](https://avatars.discourse-cdn.com/v4/letter/o/8baadc/32.png) [@owenb79](https://community.victronenergy.com/u/owenb79)\
**Post date:** [24 January 2025 23:16 UTC](https://community.victronenergy.com/t/2-times-multiplus2-on-a-3-phase-connection/19843/6 "2025-01-24T23:16:39Z")

</div>

Do you have net metering and export limits? I have 2 phases and use 3 multiplus different batteries and sizes. I use 1 shelly 3em to monitor the grid. They are all running venus OS on rpi or cerbo. I have them set to manage all phases and not the invidual phase they are connected. It took a lot to setup but very impressive to watch them share the load and charge from excess PV grid connected solar.

---