2 Multiplus2 on 3 *230V grid

Dear all.

I’ve got already answer on this question in a previous post BUT.. an engineer very experienced with Victron told me that a configuration 1 multiplus on L1-L2 and 1 multiplus on L1-L3 (3*230V grid) IS NOT correctly working.. Is there someone who has a configuration like this in his home and is all fine working

Hello,

Of course, that won’t work. The Multiplus must always be connected between N and one phase, not between two phases, which would have 400 V between them, not 230 V.

You can certainly use two Multiplus units, one on L1 and one on L2 — each connected to N.

L3 then left unused…

Or do you have a split-phase system? Please provide more details about the grid configuration and what you’re trying to achieve.

Broesel

So two inverters but three phase with neutral supply? When one phase is not available?

If English is not your first language, just use your language. The site auto translates.

Hey hello

The grid is a 3*230V grid, SO WITHOUT A NEUTRAL CONDUCTOR, also known as a Delta grid

Hey hello

o The grid is a 3*230V (230 VAC between all phase and NO N wire. The intention is that I should have a nearly off-grid system. I have 2 MPPT 5 KW inverters and 2 Multiplus2 5 KW and a battery from 10* Pylontech 4.8 KW each.

As mentioned a few times in similar posts, 3x230V delta grid is not supported by Victron. You wont get any official help in order to get an ESS system running on that grid form.

But if you search in the forum there have been a few attempts at this. Main issue is that the gridmeters may support the delta grid but the victron system is simply not able to work with that information. You need to trick the system, either by controlling the inverter import/export setpoint entirely thorugh an external control, or by recalculating the measured values so that they align with the expected star grid. Or you only use the total grid power, without giving the ESS any phase information.

Apart from that, since delta grid is not supported, i dont think any avilable ESS certificate would be valid.

And since you mentioned off-grid, an off-grid delta system is also not supported. You may be able to form a three phase delta system with three inverters, but i doubt they will work correctly. Even less so when using two inverters to form a three phase delta island.

AFAIK the working systems only used a single inverter, for example on L1 and L2.