# 2 AC Thor 9S in an off-grid system with 3 MP 48/5000 + 2 Fronius Symo 6.0-3

**URL:** <https://community.victronenergy.com/t/2-ac-thor-9s-in-einem-inselsystem-mit-3-mp-48-5000-2-fronius-symo-6-0-3/63701>\
**Category:** DIY\
**Tags:** fronius, byd, cerbo\_gx, multiplus-ii, professional, offgrid, cerbo-gx\
**Created:** [8 October 2026 16:53 UTC](https://community.victronenergy.com/t/2-ac-thor-9s-in-einem-inselsystem-mit-3-mp-48-5000-2-fronius-symo-6-0-3/63701 "2026-10-08T16:53:04Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![Geraldusmagnus](https://avatars.discourse-cdn.com/v4/letter/g/a3d4f5/32.png) [@Geraldusmagnus](https://community.victronenergy.com/u/Geraldusmagnus)\
**Post date:** [8 October 2026 16:53 UTC](https://community.victronenergy.com/t/2-ac-thor-9s-in-einem-inselsystem-mit-3-mp-48-5000-2-fronius-symo-6-0-3/63701/1 "2026-10-08T16:53:04Z")

</div>

Hello everyone,  
is anyone else running two My PV AC Thor 9S units in an off-grid system, and if so, how have you configured them?  
Via Modbus TCP, i.e. by entering an IP address in the AC Thor, or purely via frequency-dependent control?  
The three MultiPlus units only provide a total of 15 kW, while the Fronius units are supposed to provide the main share.  
So my question is: if I let the Cerbo control it via Modbus, will it regulate things knowing that there are two Fronius units connected to the system, and later even three, or do I have to use frequency control only?  
As I said, it’s an off-grid system.  
Many thanks,  
Gerald

---

<div class="post-metadata">

**Author:** ![M\_Lange](https://dub1.discourse-cdn.com/victron/user_avatar/community.victronenergy.com/m_lange/32/16_2.png) [@M\_Lange](https://community.victronenergy.com/u/M_Lange)\
**Post date:** [8 October 2026 16:57 UTC](https://community.victronenergy.com/t/2-ac-thor-9s-in-einem-inselsystem-mit-3-mp-48-5000-2-fronius-symo-6-0-3/63701/2 "2026-10-08T16:57:43Z")

</div>

In an island system, this currently only works via frequency.  
You’ll then have to match the frequencies to each other.

Work is also under way to integrate My-PV into Opportunity Loads, which would allow control via Modbus, as far as I know.